Hi to all,

I am struggling to connect up extractor fan Helios ELS-VNC 100. I would like that fan to be switched with lighting circuits and overrun for 6 minutes. Could you advise which terminals should be used for connection please?
Could you explain difference with operation by terminal 1 and terminal 3 please?

Thanks
 
That's a nice sophisticated fan you have there!
For what you want, you just need to connect permanent L and N to the terminals marked as such, and connect the L from the light to terminal 3.

1AAB8BE5-2133-4AA7-A462-A8C4AC5F68A1.jpeg
Pin 1 is to connect a switch to turn off the automatic function. I don't think you need to connect anything to that.
The application of L to pin 3 (ie turning on the light) is what will start the fan. The removal of L from pin 3 (ie turning off the light) will start the interval timer, and the fan then runs for 6 minutes (default factory setting) using the permanent L feed.

The timer period is selected by DIP switches, along with some other parameters. Sounds like you need to set the switches before you finally install the fan.

113AA154-6118-4E23-B7B8-E12F3F894CEE.jpeg
 

Reply to Extractor Fan Helios ELS-VNC 100 connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
325
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
367
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock