Discuss Extractor fan relay for two independent light switches in the UK Electrical Forum area at ElectriciansForums.net

metanet

DIY
Reaction score
0
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan serves two bathrooms, just needs to be activated from two different switched live lighting circuits.
I'm aware double pole light switches could be used in this scenario but the light switches didn't pass wife test.

Anyone know of a dual input relay I could use for this purpose?

Thanks
Meta
 
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan serves two bathrooms, just needs to be activated from two different switched live lighting circuits.
I'm aware double pole light switches could be used in this scenario but the light switches didn't pass wife test.

Anyone know of a dual input relay I could use for this purpose?

Thanks
Meta
Just use a double pole single gang switch, it's much easier.

Or if you're adamant on not using switches, then you could use a two input solid state relay.
 
Last edited:
Still cant see point of using 2 relays though
Well lets say I needed to do the above job, I've just been on google, typed in dual input relay and then clicked products, this is what came up.


I'm none the wiser which relay I should buy out of that lot, so I can either take a guess and end up with the wrong thing costing me a days work or I could buy 2 relays and do it that way very easily. Is that a good enough point.
 
Well lets say I needed to do the above job, I've just been on google, typed in dual input relay and then clicked products, this is what came up.


I'm none the wiser which relay I should buy out of that lot, so I can either take a guess and end up with the wrong thing costing me a days work or I could buy 2 relays and do it that way very easily. Is that a good enough point.


I can't see how using a pair of relays/contactors are going to be in any way easy.

They would need to be mounted properly in an enclosure that's suitable.

Contactors in the consumer unit is going to be no easy task and also costly.

The easiest, cheapest, quickest, and Compliant way is to use a pair of 1 gang dp switches as already said.
 
Well lets say I needed to do the above job, I've just been on google, typed in dual input relay and then clicked products, this is what came up.


I'm none the wiser which relay I should buy out of that lot, so I can either take a guess and end up with the wrong thing costing me a days work or I could buy 2 relays and do it that way very easily. Is that a good enough point.

Why don't you try "two input solid state relay", like i posted #7


8_1940584351.jpg
 
Sorry, no diagram, but here goes.
Relay coil to one light S/L, relay pulls in when that light is on.
Contact (needs to be C/O) common to fan S/L input.
Connect contact N/O to same S/L as coil.
Connect N/C contact to S/L on other light.

Switching one light on pulls in the relay, changes over the contacts, and applies live to fan control. Fan runs.
With that light off, tge fan is controlled by the other light as if the relay wasn't there.

The above assumes bith lights on same circuit. If on different circuits, relay coil S/L & N come from one circuit. The N/O contact must connect to the permanent L the fan is connected to - needs an extra cable core.
 
Oh yes, the relay will hum when on. It's possible to add a couple of diodes so the coil operates on DC, and it's inductance will smooth out the half wave and eliminate the hum.

Also, depending on the fan, it may be possible to just use two diodes so when either light is on, the fan control input is fed with half wave DC. This will be sufficient to trigger the timer on many fans.
 
Sorry, no diagram, but here goes.
Relay coil to one light S/L, relay pulls in when that light is on.
Contact (needs to be C/O) common to fan S/L input.
Connect contact N/O to same S/L as coil.
Connect N/C contact to S/L on other light.

Switching one light on pulls in the relay, changes over the contacts, and applies live to fan control. Fan runs.
With that light off, tge fan is controlled by the other light as if the relay wasn't there.

The above assumes bith lights on same circuit. If on different circuits, relay coil S/L & N come from one circuit. The N/O contact must connect to the permanent L the fan is connected to - needs an extra cable core.
IMG_2815.jpg
 

Reply to Extractor fan relay for two independent light switches in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
230
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
608
I'd like to find a timer switch, in a style that looks alright next to decora light switches, to control a bathroom fan. The bathroom fan...
Replies
1
Views
912
Hello all.. I have been asked to wire a relay into a FCU for a 3kW immersion. The plan is for the customer to be able to access the immersion...
Replies
17
Views
2K
Hi all, wonder if someone can help me. I've bought a bathroom extractor and I do have the wiring there already (previous extractor was there) but...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock