- Reaction score
- 17,088
https://www.youtube.com/watch?v=rnvNfI__kYUThe 0.05 figure is just the value that is acceptable for a connection. So if you fit an earth clamp to a copper pipe, the value between the conductor connected to the clamp terminal and the pipe it's connected to should be no more than 0.05ohms. It's to confirm the connection is good. If you had a 70m run of 10sq.mm, it's not going to measure 0.05 ohms end to end is it.
There is a thought/recommendation that if you earth conductor is more than 25meters in length the you could up the csa from 20mm to 16mm (see link)