Discuss questions for installation cert in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Hi ,

Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers.

1. maximum disconnection time for a type A rcd on a consumer unit at times 1 setting?

2. on a ring continuity test the readings i measured and put on cert were L-L 0.36 N-N 0.29. I have been told this is unacceptable as the difference can't be more that 0.05 ohms between L-L and N-N. Is this correct and if so where would i find this in the regs or onsite guide?


Thanks
 
1. Assuming it is 61009 or 61008 then 300ms.
2. I don't believe there is a requirement stating this but morevrule of thumb. Your readings do warrant some investigation.
 
The 0.05 ohms comes from the OSG, I have not seen it in the regs book. Certainly if the readings obtained were for intial verification tests as suggested by the thread title they would not be acceptable, I would not be overly concerned however if these readings were on an existing circuit as part of an EICR.
 

Reply to questions for installation cert in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
272
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
844
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
738

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock