Discuss Failed am2 on swa circuit? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Reaction score
0
Hi all, I recently failed my installation of swa cable and TP&N socket outlet and not sure why. Passed the rest. Any advice, It says:

-did not complete connections/terminations to industry standards

-identification/labelling to the required standard.
 
i presume that the swa used was 4 core?


L1 brown
L2 black
L3 grey
N blue

if you have got the colours in the wrong terminals, it would be a fail.

earth (cpc) needs to be well terminated to the gland via a banjo and a nut/bolt or by another standard connection such as an earthing (piranha) nut.

right size crimp on the cpc link
identified link as PE with tape or sleeve

no exposed copper showing from the terminals.

as above, was the right gland used and correctly installed?

the only person that can tell you where you went wrong is the examiner, have you asked them?
 

Reply to Failed am2 on swa circuit? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
359
Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
839
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hey all, First post but have read up a lot over the last few months as I have been prepping for my AM2s which I sat last week and thought I done...
Replies
4
Views
3K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock