Hello Guys I am new to the forum

I was looking for a little advise if possible. My bathroom fan isolation switch has cracked & was looking to get it replaced. I isolated the supply and inspected it. As it looked very simple to replace I purchased a new switch. The new switch arrived but it has a different configuration on the back to the old one.

The old configuration on the top row (off) from left to right is L1, L2, N,
The bottom row (on) mirrors the top row L1, L2, N,

The new switches rear configuration looks very different & does not mirror one another

The top row (off) has four terminals (L2 blanked) Lcom, L1, (L2 No screw), Lcom
The bottom (on) four terminals (L2 blanked) L1, (L2 No screw), Lcom, L1

I seem to have 3 x Lcom's (2 on the top row & 1 on the bottom row)
3 x L1's (1 on the top row & 2 on the bottom row)
with no L2's as they have no access to them & are blanked off.

Can anyone advise as to which wire goes to which terminal?
It is 4 core cable Live (brown), switched live (black), Neutral (grey) & earth (terminal block)

Many thanks
 
It sounds like you have got a very cheaply made switch, they have used the workings and backshell of a 3 gang switch, removed the unused L2 screws and just put a different front on it.

There should be some markings to indicate which com connects to which L1, but they normally go in order.

So starting from on side of the switch the first com at the top switches to the first L1 at the bottom, the L1 at the top in the middle switches to the com in the middle at the bottom and the second com at the top switches to the second L1 at the bottom.

Match the order of the connections as they are on your existing switch and it will work.

So for the top row reading from the left connect L, SL then N
Then on the bottom row repeat this order again starting from the left L, SL, N

If the new switch is metal then you must connect an earth to it.
 
It sounds like you have got a very cheaply made switch, they have used the workings and backshell of a 3 gang switch, removed the unused L2 screws and just put a different front on it.

There should be some markings to indicate which com connects to which L1, but they normally go in order.

So starting from on side of the switch the first com at the top switches to the first L1 at the bottom, the L1 at the top in the middle switches to the com in the middle at the bottom and the second com at the top switches to the second L1 at the bottom.

Match the order of the connections as they are on your existing switch and it will work.

So for the top row reading from the left connect L, SL then N
Then on the bottom row repeat this order again starting from the left L, SL, N

If the new switch is metal then you must connect an earth to it.

Thank you Dave for your advise it's greatly appreciated.
Now it make sense. I will let you know how I get on tomorrow once I'm back home.
I did buy the switch from an electrical wholesaler so I probably will return it.
It's a plastic switch in plasterboard wall.
Best regards
 
Out of curiosity, do you know what make/model you got?

The most recent one I bought was, I think, one of these:
https://www.NoLinkingToThis/p/briti...solator-switch-white-with-white-inserts/69862

It was easy to get and actually labelled as "fan isolator" so others would know its purpose in life!
[automerge]1589052992[/automerge]
On second thoughts it was rounded edge, so maybe this one:
https://www.NoLinkingToThis/p/briti...solator-switch-white-with-white-inserts/928ht
 
Thank you PC1966 for your advise. Funny enough after reading Dave's comments I went online & purchased the exact same model from screwfix. Though I had to buy the square edged version as the slimmer profile was out of stock for collection today.
Thank you again
Best regards
 
Hopefully that is now a quick and easy fix!

The wiring is straightforward just as you originally identified, typically with the earth joint as part of the back box.
 

Reply to Fan isolation switch configuration error in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am trying to replace my old white light switches for nice chrome ones but the wires are all red but the new switch has only l1 l2 top and...
Replies
6
Views
685
Hi all, After a bit of diy advice….(I’m in the UK) I’m trying to replace some grid switches for the washing machine from white to steel ones...
Replies
9
Views
3K
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
658
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
580
I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
356

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock