Discuss Fault finding advice in the UK Electrical Forum area at ElectriciansForums.net

dg2908

-
Reaction score
0
I got asked to find an occasional fault by a regular customer of mine. I'm now totally stumped.

This is how the relevant part of the installation stands today...
Code:
[ Main House ]  5m T&E  [ Conservatory ]     30m SWA    [ Garden ]  20m T&E in conduit [ Greenhouse    ]
[ CU - Non   ]----->----[ CU           ]-------->-------[ IP56   ]----------->---------[ 2 way CU with ]
[ RCD side   ]          [ all RCBOs    ]                [ Socket ]                     [ RCD main sw   ]

Split load main board, half RCD half not. Fault causing RCD to trip. Narrowed it down to Greenhouse circuit on Conservatory CU. When I get there problem has gone - IR and Zs on the greenhouse circuit fine.

To reduce the impact of this occasional fault, I offered the option to replace the conservatory CU (old BS3036 fuse wire) with a board of separate RCBOs, and change the feed to the Non-RCD side of the main CU as the submain is run on the surface. Customer took me up on that. On the day when I installed the new conservatory CU, the IR, Zs, and RCD tripping times on the new CU were fine.

Few weeks later he calls up, has realised that at some point the greenhouse RCBO has tripped. By the time I get there, the RCBO will reset and the IR, Zs, and RCD tripping times on the greenhouse circuit were fine. I swapped out the RCBO for his peace of mind.

Few weeks later he tells me it's tripped out and I get there after a period of wet weather, hoping this will help find something. I test the Garden Socket-Greenhouse cable. IR fine. I test the Conservatory CU-Garden Socket cable which has low IR. We agree to replace this cable (was buried 2.5 T&E under a patio etc) with 4mm SWA round the edge of the garden. All tests out fine.

Three weeks later I go to do another job there and I'm told it's tripped out again. RCBO won't reset. I disconnect the supply into the Greenhouse CU and put it into terminal blocks. RCBO Still won't reset so the problem is between the Conservatory CU and the greenhouse. I disconnect the Garden socket-Greenhouse cable at the garden socket, so the circuit is just the new SWA and the garden socket. RCBO resets no problem. I then test the IR of the Garden socket-Greenhouse cable and it's fine. I admit I'm stumped.

Long story short, RCBO trips with the Garden socket-Greenhouse cable connected even if it's IR is fine and there's no load connected to it. I have triple checked all connections! Anybody able to provide pointers as to what I can do next?
 
damp. IR at 1000V. use a hair dryer on external accessories etc.
 
yeah. 1000V IR tester is a man's toy. if boys ain't got the balls...........
 
RCBO trips with the Garden socket-Greenhouse cable connected

What was the result of the test at the consumer unit for the offending Rcbo,that you carried out with the load circuit disconnected ?
 
My IR tests were done at 500V so I will probably go back and test at 1000V now.

Des, which test are you referring to? I didn't record any results that seemed obviously fine during my faultfinding sessions
 

Reply to Fault finding advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
838
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi A professional electrician installed power to an outside greenhouse about 6-7 years ago. The supply has very recently developed a recent RCD...
Replies
6
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock