Discuss Fault finding weird issue in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi all,
Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern.

Nailed down a potential leg between 2 sockets ( 0.01 ohms on IR test) and temporarily replaced it to get the radial circuit (2.5mm on 20a B curve) to get it back on for the night.

Once replaced the circuit now stays on but trips when any item is plugged in (everything is out of the sockets beforeha

I’ve tested the RCD for nuisance tripping and X1 times which are okay. I’m running out of ideas here… okea
 
If it wasn't tripping immediately a load is plugged in and it is now then it's obviously something to do with the wiring you've altered. I'd guess there's a contact between neutral and earth somewhere but honestly I'd suggest you just pay an electrician for an hour of his time to get it sorted out safely. The fact you've energised the circuit without fully testing it is worrying and likely to be dangerous....please just get a spsrky in to check it out.
 
If it wasn't tripping immediately a load is plugged in and it is now then it's obviously something to do with the wiring you've altered. I'd guess there's a contact between neutral and earth somewhere but honestly I'd suggest you just pay an electrician for an hour of his time to get it sorted out safely. The fact you've energised the circuit without fully testing it is worrying and likely to be dangerous....please just get a spsrky in to check it out.
No, it stays livened up until any piece of equipment is plugged in.

I am a qualified electrician come here for advice.
 
Nailed down a potential leg between 2 sockets ( 0.01 ohms on IR test) and temporarily replaced it to get the radial circuit (2.5mm on 20a B curve) to get it back on for the night.
Once replaced the circuit now stays on but trips when any item is plugged in
I'd go back to first principles. Are you now getting clear IR test results for the circuit at the CU?
Try L+N together to E, I'm suspecting you will see a N-E issue.

You could also try removing your new link and see what happens, i.e. is there another fault beyond the one you already found.
 
Hi all,
Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern.

Nailed down a potential leg between 2 sockets ( 0.01 ohms on IR test) and temporarily replaced it to get the radial circuit (2.5mm on 20a B curve) to get it back on for the night.

Once replaced the circuit now stays on but trips when any item is plugged in (everything is out of the sockets beforeha

I’ve tested the RCD for nuisance tripping and X1 times which are okay. I’m running out of ideas here… okea
OK - this isn’t a difficult circuit to fault find and just needs some patience and methodical analysis. You know the circuit and you know the outlets - so you know which is the last one. At 0.01Ohms you don’t have an IR issue - that’s basically a dead short (so see what you read on continuity). You either have an appliance plugged in still or you have cable damage. So work methodically along the circuit, removing each accessory as you go and testing the next leg of cable, and you will eventually discover either the mystery appliance or the damaged cable (or possibly a mis-wired socket). You can’t not - there’s nothing else left!! You might also then consider once you’ve put it all back together about replacing that RCBO as it will be ‘tired’ from so much tripping.
 
One other possibility does occur to me….. check if this circuit wasn’t originally part of a ring that got split because of some OTHER fault (the tell would be if you have two 20A radials on otherwise identical circuits) - that repair by a previous sparks could have been bodged and an interconnect between the two ‘new’ circuits could be left hidden.
 
Or, I had this one yesterday on a floodlight fitted a number of years ago, by a family member of my customer, which never worked, it would trip the rcd as soon as you flick on the switch for it. I wonder why???
 

Attachments

  • 20231025_093141.jpg
    368.8 KB · Views: 17
update us @Georgemidnight when you discover the problem (even if it's something silly you've missed, we all make mistakes). We'd all be interested to know and it's mildly frustrating when you don't get closure.
What are your new IR results since you put your new leg in? Also, what are the IR results between (L-E, N-E or L and N combined to earth)?
 
No, it stays livened up until any piece of equipment is plugged in.

I am a qualified electrician come here for advice.
Unlike an OCPD like an MCB, a residual current protective device won't trip even if there is a fault unless there's a load plugged in and some current flowing.
 

Reply to Fault finding weird issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
294
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
847
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
355
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock