Hi, I’m just wondering what sort of readings I can expect for faults on a multimeter? I’ve only ever used a multifunction tester. What readings can I expect for a short cct fault or a polarity fault? I know that open cct will be 0L/1, cheers
 
Hi, I’m just wondering what sort of readings I can expect for faults on a multimeter? I’ve only ever used a multifunction tester. What readings can I expect for a short cct fault or a polarity fault? I know that open cct will be 0L/1, cheers

Short circuits will typically be fractions of an Ohm, but it depends how far along the circuit the short is.

Remember a multimeter is high impedance, and will not subject the circuit under test to a load (several mA) like an MFT resistance test will. Try measuring with your probes held together, then try with a few metres of cable between them. Remember that contact resistance between probes and the cable will have an effect.

Polarity can be determined by either continuity measurements or measuring using the VAC range.

Ensure your multimeter is decent quality and has a suitable CAT rating for mains voltage measurements.

And yes, open circuits will be infinite resistance - different meters have different methods of showing this.
 
Short circuits will typically be fractions of an Ohm, but it depends how far along the circuit the short is.

Remember a multimeter is high impedance, and will not subject the circuit under test to a load (several mA) like an MFT resistance test will. Try measuring with your probes held together, then try with a few metres of cable between them. Remember that contact resistance between probes and the cable will have an effect.

Polarity can be determined by either continuity measurements or measuring using the VAC range.

Ensure your multimeter is decent quality and has a suitable CAT rating for mains voltage measurements.

And yes, open circuits will be infinite resistance - different meters have different methods of showing this.
Thank you👍🏻
 
Multimeters tell it like it is... the actual readings of resistance shouldn't be any different to those you would get with an MFT. Obviously the megohm ranges can read resistances in the same order as the lower end of an insulation tester scale but do not subject the insulation to a high test voltage.

What might differ are readings of AC ghost voltages on cables that are not actually energised but are picking up a whiff of capacitive leakage from live cables nearby. Ghost voltage readings are not useful or informative, but can be surprising, e.g. if you find 100V on a cable that's known to be disconnected. Because the multimeter input circuit tends to have a high input resistance, they can read voltages (which are correct) in situations where the lower input resistance of an electrical tester would bleed off the leakage and not register very much. Both instruments are correct, but the multimeter reveals the ghost voltage better.

I would mainly use the multimeter to trace faults, other than to test insulation which needs the MFT.
 
Multimeters tell it like it is... the actual readings of resistance shouldn't be any different to those you would get with an MFT. Obviously the megohm ranges can read resistances in the same order as the lower end of an insulation tester scale but do not subject the insulation to a high test voltage.

What might differ are readings of AC ghost voltages on cables that are not actually energised but are picking up a whiff of capacitive leakage from live cables nearby. Ghost voltage readings are not useful or informative, but can be surprising, e.g. if you find 100V on a cable that's known to be disconnected. Because the multimeter input circuit tends to have a high input resistance, they can read voltages (which are correct) in situations where the lower input resistance of an electrical tester would bleed off the leakage and not register very much. Both instruments are correct, but the multimeter reveals the ghost voltage better.

I would mainly use the multimeter to trace faults, other than to test insulation which needs the MFT.

Thanks Lucien for correcting my error. Of course I should have said that it is voltage readings that will be different with a high impedance meter.
 
Ah, hadn't noticed that, was only replying to the OP. I won't make a charge on this occasion.
 

Reply to Fault finding with a multimeter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...
Replies
19
Views
1K
Hi I'm trying to find if I have a fault in these to brakers of in the lines. The 32A braker leads as far as I know only to a junction box that use...
Replies
18
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
730
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock