Discuss Fault on domestic home wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
110v from switch to switch (see attached picture), tn-cs system with 30mA RCD in Place, trips fine when tested at 100% and 500% customer complained of getting shocked when touching both switches at once but doesn’t trip with this fault, have a few theories, but any suggestions?

514258D2-9701-4C38-8195-170B5A64DE7A.jpeg
 
Possible poor or no earth at one of those switches, therefore creating a potential difference. Chances are it’ll be the light switch that isn’t earthed properly as there’s more connections throughout the circuit to come loose.
 
I haven’t had a chance to do any tests yet apart from very quickly testing the rcd, with the customer away im not going asap I’m going to get there this week at some point, what’s concerning me is why the rcd never tripped? As even if there was a loose earth connection, or no earth atall surely the rcd should still of picked up an imbalance between live and neutral and tripped regardless when the customer touched the switches?
 
I had similar ages ago, customer getting intermittent tingles from metal dimmer switch, no voltage between plate & known earth mind.

I left her to fry, whilst consulting members here (nahh not really, swapped switch to plastic). Went back to investigate with new advice and found there was no continuity between installed switch cpc & earth terminal in CU.
 
I haven’t had a chance to do any tests yet apart from very quickly testing the rcd, with the customer away im not going asap I’m going to get there this week at some point, what’s concerning me is why the rcd never tripped? As even if there was a loose earth connection, or no earth atall surely the rcd should still of picked up an imbalance between live and neutral and tripped regardless when the customer touched the switches?

Just shows why you shouldn't have an over reliance on RCD's. Guess the flow through her etc to Earth, was enough to give a tingle, insufficient for imbalance. Dunno, forum boffins will say.
 
I'd suspect that the earth connection somewhere is missing (as mentioned probably on the lighting circuit) and you have a low Insulation resistance between L&E. If so, your need to check the whole circuit thoroughly as you have no idea where the fault is. The CPC could be broken to the first light in the circuit and other metal light fittings and accessiores may potentially be live too !
As RCDs only work on earth imbalance maybe the touch current was below 30mA it may have been different if the customer was bare foot on a damp floor either way this is a potential killer.

I' be carryng out continuity and IR tests the breaking down circuits, at a guess you find a snapped CPC and a squashed Live somewhere on one of those two circuits.
 
Last edited:
I haven’t had a chance to do any tests yet apart from very quickly testing the rcd, with the customer away im not going asap I’m going to get there this week at some point, what’s concerning me is why the rcd never tripped? As even if there was a loose earth connection, or no earth atall surely the rcd should still of picked up an imbalance between live and neutral and tripped regardless when the customer touched the switches?

Maybe time to review how rcd's work ...
 
Capacitive coupling or inductance between the earth and other cables can be enough to measure 100v and feel a tingle. But if you measured the current discharged it would be tiny. Switch mode PSUs tend to have a bit of earth leakage which will often appear as half mains voltage if they aren't properly earthed.

So first port of call should probably be earth loop impedance test at switch/earth continuity test.
 

Reply to Fault on domestic home wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
832
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock