Discuss Fault on underfloor heating mat. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Hi All

I have a fault on an underfloor heating mat which is as follows

L-N no continuity (should be around 200 ohms)
N-E short circuit
L-E clear

I need to find the exact location of the fault so I can take a tile up to repair it, I have thought about hiring a thermal imaging camera, just wondering if anyone has any other ideas?

Cheers
 
it's a non-metallic needle ina haystack.there are specialist companies with the gear to find this, but is it worth the effort? personally, i'd rather buy a pair of socks.
 
How do you find the fault with a thermal imaging camera?
10mins of constant IR testing at 1000v to warm the dead short up or is there a specialist bit of equipment you can use ?
 
If there's no continuity L to N then it is completely open circuit and will not heat up. So there will be nothing for the thermal image camera to pick up.
 
L-N no continuity (should be around 200 ohms)
N-E short circuit
L-E clear

There is a certain 'less than safe' way to locate the problem area with the fault you have... It involves disconnecting some things, and connecting other things (ideally through an isolation transformer) to a variac, then winding it up while monitoring the current with a clamp meter to ensure the section of element that is connected is not overloaded. When it starts heating the problem area should be locatable with a thermal imaging camera.

Don't ask me how you repair the damaged part though. Just trying to access the element from under the adhesive can cause more damage, especially if the insulation is soft silicone. Far better to replace the entire element, or just do without.
 
Freddo, good idea locating using the N-E short rather than the open circuit. Pretty likely both issues will be at the same location. I should have thought of that.
 

Reply to Fault on underfloor heating mat. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
394
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
467
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
275
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock