Discuss Faulty Air source heat pump in the Solar Thermal Advice Forum area at ElectriciansForums.net

jimbro

-
Reaction score
3
My NIBE F2015 air source heat pump which is only 7 years old has an apparent fan motor failure. The fan turns freely and the motor starter capacitor has been replaced but the unit will still not run. Any suggestions for a fix?
 
Why was the capacitor replaced, was the motor and its control tested to verify it was at fault.
 
What controls the motor? Contractor/Relay? If it were me I’d be pushing the contactor In and seeing if it ran. If it does then you’ve got s control issue. If not then bell the windings our.
 
On an ASHP I'd guess the motor would be speed controlled according to head pressure (condensing temp/ambient temp). Not sure if it would be inverter speed control or multiple wound motor though.
 
Thanks for all the help. The unit was tested and showed power was being supplied to the fan motor windings through the controm relays. The connector at the fan motor was tested live showing full mains voltage on both windings. A Nibe installer replaced the starter capacitor which made no difference and Nibe have now agreed to replace the motor.
 

Reply to Faulty Air source heat pump in the Solar Thermal Advice Forum area at ElectriciansForums.net

Similar Threads

After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
673
We have just completed a self build, and heating system is Air Source Heat Pump, unvented HW cylinder, Buffet Tank, all Vaillant equipment. The...
Replies
0
Views
1K
Hello , I’m trying to further my knowledge into UFH/Rad/HW valves heating systems with air source pumps. What is normally needed outside with...
Replies
0
Views
598
I need advice regarding an electronic problem on my Hayward Power-flo Matrix pool pump. I notice that : 1. Neutral wire from source has become...
Replies
4
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock