Search the forum,

Discuss Faulty extractor fan in the UK Electrical Forum area at ElectriciansForums.net

JB8888

DIY
Reaction score
15
Hello,

We moved into a new property 5 months ago and there is an extractor fan in the bathroom that has never worked. This weekend I decided to have a crack at fixing or replacing it. I'm new to DIY so bear with me here!

Firstly, there is no isolator switch for this fan as far as I can tell. I've looked everywhere including climbing up into the loft.

I took apart the new fan and there was a blue wire, and brown wire and then a wire that had been stripped coming out of the wall. I know that blue is neutral and brown is live and from my limited reading I THINK the stripped wire is the 'switched live' wire which has something to do with the timer? The neutral and live wires were connected to the fan itself but the stripped wire was not.

There was no earth wire - should there be?

Anyway, I wired in the new fan, linked the three available wires as follows:

Blue wire: N
Brown: L
Stripped: SL

Turned the light on and nothing happened. Is it possible these wires have been completely disconnected from the mains or have I made a rookie error somewhere?
 
The bare wire is the cpc aka the earth. Just wants sleeving and putting in a connector out the way. Yes blue is neutral, and brown is line/live. Link that terminal to the switch line terminal and it should work, it wont run on and probably didnt have those terminals linked before hense not working
 
agree with above.probably not wired for a timer fan, so link the L an S/L terminals with a bit of wire
 
The bare wire is the cpc aka the earth. Just wants sleeving and putting in a connector out the way. Yes blue is neutral, and brown is line/live. Link that terminal to the switch line terminal and it should work, it wont run on and probably didnt have those terminals linked before hense not working

Thanks for your reply! There is already a wire coming out of the terminal going into something labelled SL on the new fan (there wasn't on the old fan).

So I just tried again and now the earth wire has been tucked away and the neutral and live wires have been placed in the neutral and live ports in the terminal.

Coming out the other side of the terminal is a blue neutral wire, a brown live wire and a black one labelled SL which is now opposite an empty space on the terminal (where I previously and incorrectly had the earth wire).

Still isn't being triggered by the light. Should there be an input to that empty terminal?
 
You need to put an additional little link wire yourself between the switch live terminal and the live terminal that has your brown wire in.. this is obviously all assuming you have voltage present
 
You need to put an additional little link wire yourself between the switch live terminal and the live terminal that has your brown wire in.. this is obviously all assuming you have voltage present
i told him that in post#3.
 
I'm just hoping he's isolated the circuit...:eek:
It may be just s/l and n......but how is he supposed to know that?
A bit scary when folks talk about using a stripped wire as s/live.
 
I'm just hoping he's isolated the circuit...:eek:
It may be just s/l and n......but how is he supposed to know that?
A bit scary when folks talk about using a stripped wire as s/live.
builders and bathroom fitters do it all the time. think it's the fact they don't understand 3 core. with a pint of beer in hand, they only got a thumb and 1 finger to count with.
 
I'm just hoping he's isolated the circuit...:eek:
It may be just s/l and n......but how is he supposed to know that?
A bit scary when folks talk about using a stripped wire as s/live.
Yes don't worry I isolated the circuit. I'm a first time buyer and ashamed to say I have zero experience or knowledge of this kind of thing which is why i'm trying to learn some practical life skills - hence attempting this myself so I can learn and not be so useless in future! Thanks for your help it is appreciated
[automerge]1578240802[/automerge]
We both did, so thought third time lucky he might do it ? at least the bloody cpc is now out of the SL hole
Thank you, yes it's out ?.
As mentioned I'm a complete newbie here. There are wires for the fan itself also going into the terminal so I thought perhaps you meant that. I now realise you meant I should put a wire into the empty SL terminal and put the other end into the live terminal along with the brown wire - so two wires in one hole - is that right?

I'm well aware I'm useless at DIY, I'm trying my best to learn some practical life skills hence joining this forum. I really appreciate your help and time!
 

Reply to Faulty extractor fan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
810
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
480
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Replies
14
Views
1K
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi Just replaced a bathroom extractor fan. I didn't alter any wiring. Both old & new have live & switched live. Trouble is, once activated, the...
Replies
5
Views
391

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock