Discuss Fauna......18month old installation. in the UK Electrical Forum area at ElectriciansForums.net

Leesparkykent

Esteemed
Reaction score
9,113
Got a job I completed about 18 months ago.Big 5 bed refurb with multiple extensions so it's a full installation from scratch. Got a call this morning saying RCD won't reset, went through the usual procedure over the phone and get them to leave the circuit breaker off for the circuit in question so they can get the RCD to reset...Went there this afternoon and carried an IR test out on the circuit and it's as flat as a pancake line-earth.... split the circuit in half and still flat as pancake on both legs of the ring final circuit.... only 12 sockets on the circuit so Carry out installation resistance testing until I find the legs with the faults... 1 leg that's down is between 3rd and 4th socket and the other leg that's down is between board and last socket in the order I was testing.

It's a complete nightmare as solid wood flooring down, Laura Ashley wall paper and so on....can't turn it in to a radial because the fault between 3rd and 4th socket so I'm stuck with having to get a new leg in between 3rd and 4th socket and turning it into a radial or getting two new legs in and keeping it as a RFC. Not botherd about loading as only serves a play room, bedroom and hall way socket.

Getting the new leg/legs in is going to be disruptive but unfortunately there is no getting around it. Although it's only 18months old I think I should be charging them....spent an hour there today and I've rearranged jobs for tomorrow so I can get back in there in the morning to sort it out. They clearly have a rodent problem as two legs of a RFC just don't go down all of a sudden after 18months...what's your thoughts?
 
or possibly faulty cable. i had some SWA . 1 conductor went down (open circuit) after 3 weeks.
 
Got a job I completed about 18 months ago.Big 5 bed refurb with multiple extensions so it's a full installation from scratch. Got a call this morning saying RCD won't reset, went through the usual procedure over the phone and get them to leave the circuit breaker off for the circuit in question so they can get the RCD to reset...Went there this afternoon and carried an IR test out on the circuit and it's as flat as a pancake line-earth.... split the circuit in half and still flat as pancake on both legs of the ring final circuit.... only 12 sockets on the circuit so Carry out installation resistance testing until I find the legs with the faults... 1 leg that's down is between 3rd and 4th socket and the other leg that's down is between board and last socket in the order I was testing.

It's a complete nightmare as solid wood flooring down, Laura Ashley wall paper and so on....can't turn it in to a radial because the fault between 3rd and 4th socket so I'm stuck with having to get a new leg in between 3rd and 4th socket and turning it into a radial or getting two new legs in and keeping it as a RFC. Not botherd about loading as only serves a play room, bedroom and hall way socket.

Getting the new leg/legs in is going to be disruptive but unfortunately there is no getting around it. Although it's only 18months old I think I should be charging them....spent an hour there today and I've rearranged jobs for tomorrow so I can get back in there in the morning to sort it out. They clearly have a rodent problem as two legs of a RFC just don't go down all of a sudden after 18months...what's your thoughts?
Hi Lee how have you determined it's a Rodent causing the trouble?
 
If I've understood correctly you've found 2 N-E faults in one RFC that was installed and tested ok 18 months ago. That's pretty unusual - is it worth a bit more time to explore?
 
Bit of a punt @Pete999 but unless like @telectrix says faulty cable then I can't think what else it could possibly be. It's been in 18months and all working fine until this morning. The section of house that the RFC serves is the only section with a suspended floor. IIRC there's about and 8" void.
 
My oops too - sorry. Anywhen, I guess there's no chance to pull that cable back ? Usually the rats leave conductors exposed or bite right through them. But he could have expired on the job and be causing the issue. Out of interest, what was the IR? Is there any chance there's water in that void?

Edit - no medication here yet either. Have to wait till she goes out tonight :)
 
My oops too - sorry. Anywhen, I guess there's no chance to pull that cable back ? Usually the rats leave conductors exposed or bite right through them. But he could have expired on the job and be causing the issue. Out of interest, what was the IR? Is there any chance there's water in that void?

Edit - no medication here yet either. Have to wait till she goes out tonight :)
no chance of pulling cables etc mate and 0.00Mohm...
 
If your 100% it was tested good at installation then it is chargeable IMO and its discussion time with the client about how you fix with least amount of damage . hopefully its all in the floor voids . seek advice from a joiner whether he can lift and relay a section of floor or alternatively go through the ceiling from below .

For minimal damage repair the section between 3 and 4 and turn into a radial . If it does turn out to be rodent damage this could be just the start unfortunately .
 
If your 100% it was tested good at installation then it is chargeable IMO and its discussion time with the client about how you fix with least amount of damage . hopefully its all in the floor voids . seek advice from a joiner whether he can lift and relay a section of floor or alternatively go through the ceiling from below .

For minimal damage repair the section between 3 and 4 and turn into a radial . If it does turn out to be rodent damage this could be just the start unfortunately .
yeah that's my thoughts. It's all on the ground floor unfortunately.
 
Year and a half down the line with no previous issues I think you have good reason to charge. Misread your opening post as 8 months:eek:
 
yeah that's my thoughts. It's all on the ground floor unfortunately.

Is there any evidence of rodent infestation, i.e. tell tale droppings in the loft, they have a contract with Rentokill, with bait traps set up.

Did a job last week, spent two days in the loft. There was loads of mice pooh everywhere, but they haven't had their cables pack up yet.
 
I had a meece problem a few years back under the floor boards could hear them all night. Pulled some boards up and there was damage, not too bad so a bit of tape and will sort them one day. Bought a couple of plug in mouse scarers not holding out much hope but I swear I heard them legging it and have never been back.
 
what were the readings n - e ?

Sounds a bit of a nightmare, and to have 2 legs down is very unfortunate...... For the customers wallet!

Can you remember the exact routes of the cables?
 
Why do mice like (eating) pvc cables o_O

Cancel that, my lads dog likes chewing on plastic dog toys, guess its the mouse equivalent.

PPS you could watch this film tonite Lee, might give you some ideas :);

 
what were the readings n - e ?

Sounds a bit of a nightmare, and to have 2 legs down is very unfortunate...... For the customers wallet!

Can you remember the exact routes of the cables?
700 odd Mohm IIRC. Yeah I feel bad for the guy as he's put me on to a few other extended family members and have had 3 big jobs out of them. Might have to swallow the hit.
 
[QUOTE
Did a job last week, spent two days in the loft. There was loads of mice pooh everywhere, but they haven't had their cables pack up yet.[/QUOTE]

Had similar last week, very old mill and mouse poo everywhere in the attic. Commented to the owner and he told me to look up. There were a couple of clumps of bats roosting and it was their poo. Apparently bat and mouse poo can look similar but feel and taste different!
 
Lee, I assume the two dodgy legs test dead short L-E with both sockets at either end completely removed ? And no evidence of dodgy DIY -like attempting to refix skirting or anything like that ? But I reckon you're right being as it's a ground floor void where the cables run. Funny thing I've noticed with gnawed cables is that most times the outer sheath has been chewed on the neutral side, wonder if the rats/mice can sense it , or do they have little voltsticks ? :D
 
[QUOTE
Did a job last week, spent two days in the loft. There was loads of mice pooh everywhere, but they haven't had their cables pack up yet.

Had similar last week, very old mill and mouse poo everywhere in the attic. Commented to the owner and he told me to look up. There were a couple of clumps of bats roosting and it was their poo. Apparently bat and mouse poo can look similar but feel and taste different![/QUOTE]

Batman wasn't visible, think I would of seen him!
 

Reply to Fauna......18month old installation. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
516
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
313
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
2K
I was asked to see why a set of sockets weren’t working in the house (which appear to be a ring circuit based on breakers) There was no power on...
Replies
27
Views
1K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock