Hi all, having a problem on a job...
Using a switched FCU to control some LED under-cabinet strip lights. Customer reported that the lights were staying on after the FCU had been switched off. So I thought the FCU must be stuck in on position, so I replaced the unit.
Had a call from the customer today reporting the same problem.
Upon inspecting the original FCU, it appears to be working as it should. I.e. it isolates both live and neutral.

Any ideas?
Thanks in advance.
 
i suspect capacitance . a snubber may help.
 
possible. it's quite common for GU10 LEDs to stay faintly lit or flash after switch off. capacitance or induced voltage from adjacent live cables. a snubber draians the unwanted voltage away.
 
try a 1 watt resistor, value around the 200Ω mark across the ELV feed to the strip
 
Hi all, having a problem on a job...
Using a switched FCU to control some LED under-cabinet strip lights. Customer reported that the lights were staying on after the FCU had been switched off. So I thought the FCU must be stuck in on position, so I replaced the unit.
Had a call from the customer today reporting the same problem.
Upon inspecting the original FCU, it appears to be working as it should. I.e. it isolates both live and neutral.

Any ideas?
Thanks in advance.

My idea is that it may have been wise to test the suspected "faulty" FCU BEFORE you went to the trouble and expense of replacing it. ;)
 
To Geordie Spark: I had this problem with an FCU before, admittedly an LAP one. So thought it would be prudent to take a replacement with me and just swap it.
The FCU in question this time is a BG one, which are usually alright.
Had no end of trouble with LAP bits in the past, so will not use anymore!
 

Reply to FCU and Led under-counter light problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hello all have a couple of questions re-some decking lights. I have fitted by Electrician around 10 years ago, He’s spured off an existing...
Replies
3
Views
821
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
791
Sure this has been answered before, can’t find a specific answer though. My house was rewired in 2021 and as part of the rewire I had LED lights...
Replies
4
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
534
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock