Discuss Filed Socket - Cracked and no switch longer toggles in the UK Electrical Forum area at ElectriciansForums.net

Clearly heat damage due to arcing. Maybe you had a tumble dryer or similar on the socket previously? That may have set it up for failure with a kiln running. As your kiln is at least five years old it could be the thermstat is not working so will and it runs hotter for longer than it should??? just speculation on possible causes other than purely a crap socket. Mk or Crabtree are pretty robust although MK have deteriorated in quality in some ways over the last few years.
The circuit has only run the kiln and was installed in the new studio last September. But you do make a good point on the kiln condition, the coils have yet to be changed and are starting to sag so this could have placed additional load/pressure.

I think it is time to get the coils changed
 
The circuit has only run the kiln and was installed in the new studio last September. But you do make a good point on the kiln condition, the coils have yet to be changed and are starting to sag so this could have placed additional load/pressure.

I think it is time to get the coils changed
get it tested first. saggy coils are 1 thing, electrical faults another. it'slike old t!ts. even saggy ones still work.
 

Reply to Filed Socket - Cracked and no switch longer toggles in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
961
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
625
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
819
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
I have an inground pool with a 22 year old, 120vac light fixture in a niche connected to water-holding conduit running to a switch in an...
Replies
7
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock