Man that was a tough day!
It needs a rewire!!!
Sockets off the lighting circuit.
Spurs off spurs (ring).
Shed spurred from a socket with multiple sockets in it and then to another shed!
And thats all in addition to the IR issues and broken CPC.
However one thing I could do with some help on is the following..
Broke the ring at the CU and the boiler FCU (on ring).
Leg A shows 1.1Mohm N-E
Leg B shows 20Mohm
Cable going into boiler shows 0.9Mohm
When I connect the cables in the boiler FCU back together I get 0.6Mohm N-E (with the boiler switch off) and 0.4Mohm with the boiler switch on??