Morning all..
I have a bugger of a ring problem to solve on monday. All the following faults are on the one ring.
It has a N-E IR fault which I have almost found.
It has an intermittant tripping 32A MCB which looks like an overloaded circuit (one ring for whole house) and...
It has a broken CPC.
This house is absolutely jam packed with clutter.
I can find the broken CPC by doing the following:
1. Split CPC at any socket
2. Test at CU which side has broken CPC (wander lead or R1+R2)
3. Connect line and CPC of good side of ring in CU.
4. R1+R2 all sockets - those with continuity are ok and eliminated.
5. Reconnect at broken socket and break CPC at one of the suspect sockets.
6. Go to 2 above and repeat.
However, I have a feeling from spending a little time there that the fault will be in JB. The above method will find the fault if in a socket but not if its in an unreachable JB. How can I narrow it down to between 2 sockets? (i.e the ones either side of the faulty JB). I have to say I dont like the EFLI method, I dont find it accurate enough and it leaves you even more confused.
Is it just a case of slowly working out the layout of the ring and getting an idea of where the fault might be during all the testing or is there a better way?
I have a bugger of a ring problem to solve on monday. All the following faults are on the one ring.
It has a N-E IR fault which I have almost found.
It has an intermittant tripping 32A MCB which looks like an overloaded circuit (one ring for whole house) and...
It has a broken CPC.
This house is absolutely jam packed with clutter.
I can find the broken CPC by doing the following:
1. Split CPC at any socket
2. Test at CU which side has broken CPC (wander lead or R1+R2)
3. Connect line and CPC of good side of ring in CU.
4. R1+R2 all sockets - those with continuity are ok and eliminated.
5. Reconnect at broken socket and break CPC at one of the suspect sockets.
6. Go to 2 above and repeat.
However, I have a feeling from spending a little time there that the fault will be in JB. The above method will find the fault if in a socket but not if its in an unreachable JB. How can I narrow it down to between 2 sockets? (i.e the ones either side of the faulty JB). I have to say I dont like the EFLI method, I dont find it accurate enough and it leaves you even more confused.
Is it just a case of slowly working out the layout of the ring and getting an idea of where the fault might be during all the testing or is there a better way?