Discuss Fire Alarm Circuit RCD Protection TT System in the Commercial Electrical Advice area at ElectriciansForums.net

Strima

-
Esteemed
Arms
Reaction score
5,984
Doing a board swap on a HMO property with a TT system later this week and I've been asked to add OCPD for an L1 fire alarm system.

As usual the landlord is being a little cagey with letting me know the other tradesmans details so I can confirm this but I'm on the understanding that a fire alarm must not be on an RCD protected circuit?

Is this correct for TT systems, the rod Ra is just under 200 ohms which I will be trying to get down if I can find somewhere to add an additional rod, the whole pace is concreted in.

Also what size OCPD? I'm thinking 6 amp seems to be pretty normal.
 
can't see a problem with the fire alarm being on it's own dedicated RCBO. the alarm panel or it's cabling would need to be faulty to trip the RCBO. the OCPD would be sized according to the cable feeding the alarm,usually 1.5mm FP200 so a 16A would be appropriate. no problem if you want to fit a lesser device.
 
I would be inclined to tap directly of the tails and provide this F/A with its own dedicated supply that is not subject to a common trip like the front end rcd of a distribution board, faults of other circuits should not impact on the supply to the fire alarm.
 
Last edited:
The board is going to be full RCBO but I tempted to use a 100mA S type RCD as the main switch to give it some earth fault protection.
 
I would be inclined to tap directly of the tails and provide this F/A with its out dedicated supply that is not subject to a common trip like the front end rcd of a distribution board, faults of other circuits should not impact on the supply to the fire alarm.
my garage circuit is fed from a non-RCD way in a hi integrity dual RCD house board. 40A MCB feeding 6.0mm to a sub. 4 freezers and my workbench on a 32A RFC (was a 20A radial till 'er indoors decided on a hot tub and a sauna. now defunct when she realised that the leccy bill has trebled) : might one day get round to fitting a RCBO in the sub.
 
my garage circuit is fed from a non-RCD way in a hi integrity dual RCD house board. 40A MCB feeding 6.0mm to a sub. 4 freezers and my workbench on a 32A RFC (was a 20A radial till 'er indoors decided on a hot tub and a sauna. now defunct when she realised that the leccy bill has trebled) : might one day get round to fitting a RCBO in the sub.
I think your own home installation is somewhat different in the requirements of a HMO L1 F/A installation and tbh does the 6mm supply need RCD protection, surely just rcbo the garage board to ensure each freezer is independent ... but I am just teaching you to suck eggs here aint I :)
 
Don't understand your post, it's my understanding that RCBO's give earth fault protection.
I could have been clearer, I was distracted by a bacon butty. Rather than use 30mA RCBO for the circuit I'm considering using an MCB then having upfront 100mA S Type.

I could still go with 30mA RCBO I'm just banding ideas around in my head and randomly hitting the keyboard at the same time.

Probably having a bit of a Buzz moment...
 
If the cable is installed in the wall less than 50mm etc etc then you can not use a 100mA rcd for the required additional protection, is it buried in a wall or is it surface?
Having it on its own individual rcbo and ensuring selectively with all other circuits is not an issue, especially as an rcd will be required for fault protection and if buried,
additional protection as well.
A 100mA rcd upfront protecting all the circuits is a really poor idea.
 
I think your own home installation is somewhat different in the requirements of a HMO L1 F/A installation and tbh does the 6mm supply need RCD protection, surely just rcbo the garage board to ensure each freezer is independent ... but I am just teaching you to suck eggs here aint I :)
was going to be 10mm but drill hit rebar and could only get hole big enough for 6mm. as for rcd, the 6mm is surface in mini trunking. RCBO feeding 4 freezers might be bad as if one freezer or anything i've got connected developes a fault we lose all 4 freezers. anyway, i done a RA in head.if i'm daft enough to poke into live parts, it's my funeral. ??
 
Putting in on its own RCBO is one option if it is wired in T&E or similar so the < 50mm rule applies, though if in FP cable it should be OK without "additional" protection due to the foil shield.

If worried about spurious trips not being noticed/fixed, how about taking it off a central lights circuit?

In any case I would still prefer a 100mA delay RCD up-front so a failed RCBO is not leaving the system with no viable means of disconnection on a L-E fault.
 
Putting in on its own RCBO is one option if it is wired in T&E or similar so the < 50mm rule applies, though if in FP cable it should be OK without "additional" protection due to the foil shield.

If worried about spurious trips not being noticed/fixed, how about taking it off a central lights circuit?

In any case I would still prefer a 100mA delay RCD up-front so a failed RCBO is not leaving the system with no viable means of disconnection on a L-E fault.
FP200 should be treated the same as T&E with regard to additional rcd protection.
 
It is not manufactured to BS8436.
Thanks for this info westwood10. I did not realise that FP200 is not suitable for this application. Following on from your post, I did a little research. I think it has to do with the construction of the foil shield, in that it is not capable of carrying a large fault current for long enough to operate the OCPD. Every day's a school day...
 
Putting in on its own RCBO is one option if it is wired in T&E or similar so the < 50mm rule applies, though if in FP cable it should be OK without "additional" protection due to the foil shield.

If worried about spurious trips not being noticed/fixed, how about taking it off a central lights circuit?

In any case I would still prefer a 100mA delay RCD up-front so a failed RCBO is not leaving the system with no viable means of disconnection on a L-E fault.
Shouldn't fire alarms be wired from the board in fireproof cable??
 
Shouldn't fire alarms be wired from the board in fireproof cable??
Depends if you're doing a Part 1 or Part 6 system.

HMO being commercial should really be a -1 system and would require suitably fire resistant cabling from source to main panel. This can however vary with local authority.

A -6 by contrast can be either a dedicated circuit or tapped out lighting circuit, with the cabling requirements being less onerous.

It is acceptable if the unit is purpose built (and not a converted house) to have a -1 system covering communal areas and individual -6 systems in each self contained unit (interlinking is optional due to each unit having the required about of fire durability.

I'll dig out my 5839s when I get a mo and get relevant clauses.
 

Reply to Fire Alarm Circuit RCD Protection TT System in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual...
Replies
15
Views
4K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
997
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock