hello guys

#2 Fire alarm - install in common parts, grade A category, LD2 coverage, conforming to BS 5839

A grade A fire alarm to me normally means a centrally wired system with contralised controls, so I would not get away with a wireless system with a wireless control module all mains wired?
 
You can install a wireless Grade A, LD2 system. Might be an idea to speak to a supplier who would design and specify a system for you.
 
A Grade A system is defined as a mains supplied central control unit c/w battery backup for min 48 hours (norm 72 hours), monitoring all detection and devices for fire and fault conditions. The control unit must be able to display zone area of activation and provide evacuation, silence and reset functions. All panels must meet EN54 parts 2 &4
 

Reply to Fire alarm requirements in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
Hello People Our Enphase solar system needs to have the AC supply shut down via the fire alarm contactors local input output unit that has NO &...
Replies
0
Views
484
Hi all, I currently have a Pyronix Enforcer V10 Wireless alarm system. I have some shock/contacts on windows, doors, PIRs, and an external siren...
Replies
0
Views
763
This isn't really an electrical issue as such but I know you guys are pretty tech savvy and familiar with all the latest and greatest...
Replies
13
Views
1K
Hi Guys Recently finished a new build house, 2 levels/ 5 bed. Wired AICO grade D LD2 system throughout. LABC has come to sign off saying needs...
Replies
29
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock