Discuss Fire alarm supply.... in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Reaction score
0
Hi all please help.

If you was to use galv conduit all the way from the board to the isolator next to the fire alarm panel. does the cable still need to be something like a fp200 or is normal singles ok to use ??
 
can see the scenario. in a fire, the galv. conduit will get well hot, melt the insulation on the singles. dead short to conduit. OCPD trips. no power to alarm.
 
Off the top of my head the cable has to be capable of taking 850c for 30 minutes before failing, don't think singles in galv would last that long.
 
It's common for galvanised conduit to be used for the drops in fire alarm installations. This is for impact protection though and FP200 is still used. 25mm is needed as two FP cables dropping are quite thick.
 
It's common for galvanised conduit to be used for the drops in fire alarm installations. This is for impact protection though and FP200 is still used. 25mm is needed as two FP cables dropping are quite thick.
Try Syrup of figs Mate works very well, so sorry I couldn't resist.
 

Reply to Fire alarm supply.... in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
1
Views
711
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
604
I'm installing mag-locks and fire door hold-open magnets at the moment and I'm wondering if any of the cable should be fire performance cable...
Replies
1
Views
642
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi All, Please may I ask if light fixtures must now always be fitted by an electrician? also for domestic homes, is it okay for there to be a...
Replies
4
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock