Hi there,
Done a fuseboard change today, but getting a bit confused with the Ze and Zs tests
Where are these tests done? At the DB main tails incomer, at the origin (sweated earth on incoming cable)
It is a TN-S supply and i have a 3 lead L-N-E megger loop tester.
Getting a bit confused aswell with what bonding is disconnected too.
Any help would be appreciated. Thanks.
 
The installation should not be energised till all tests are completed but just in case, Turn off, prove dead, disconnect main earth hook that up to your earth croc. Put neutral probe on neutral terminal and live probe on live then press the button the result given is Ze.
Zs is done at each point of utilisation in a similar manner with the highest reading being the one you record.
 
on the certifiacte it says Ze at origin which you have explained.
then it says on the test results page zs at db....is this a different test.
 
YEs this is a test of the circuit loop impedance which is carried out at the last point of the circuit or the mid point of the ring it is also carried out after the r1r2 test which on a lighting / radial circuit should be carried out at every point to confirm polarity at each point
 
is the db at the origin of the insulation? sometimes the DB can be at a diffrent point to the incoming service, this is probbely what its asking.
 
dont forget here as well 067256......that you will need to test twice for a single phase supply.....once for line-earth...a Ze..this will give you your PEFC at the origin of supply...and another for line-neutral...this will give you your PSC at the origin of supply and it is the HIGHEST of these two measurements that will be your PFC that you record......
 
Don't 3 lead mft's do both tests at once and only display the highest reading? Mine does but don't know about the megger. OP said he was doing a 3 lead test.
 

Reply to First proper test and inspect today. Confusion. in the Australia area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
293
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
So i've been doing electrics for several years now, and am going for my 18th edition this week. I'm 99% confident i'm going to pass it. After...
Replies
25
Views
5K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock