split load DB

Every circuit (7circuits) 1st half tripped RCCD

And two circuits second side tripped The 1st RCCD whist the second RCCD supplying these circuits remained on??

Swapped over the RCCDs to prove the units were not faulty.

Removed every neutral to prove borrowed neutral not at fault still tripped.

Any suggestions guys as I am the second sparky with a damaged ego on this one
 
Are the incoming tails tight in the DNO head and / or meter - seen this on a number of occassions.

And yes - it woud trip 1 or both RCD's ...

Have you got a clamp meter - this may give you some pointers ...
 
split load DB

Every circuit (7circuits) 1st half tripped RCCD

And two circuits second side tripped The 1st RCCD whist the second RCCD supplying these circuits remained on??

Swapped over the RCCDs to prove the units were not faulty.

Removed every neutral to prove borrowed neutral not at fault still tripped.

Any suggestions guys as I am the second sparky with a damaged ego on this one

Hi bud,not crabbing your methodology,but i would have isolated and tested the two RCD's independently,before guessing at not swapping two faulty units.

No matter who,and how many,have has looked at this problem,you need to start right at the beginning,and use the known and trusted methods,one step at a time.

These will not 100% guarantee a result,but it massively limits,what else can be happening.

As for guessing what is going on,aside from what is obvious,a whole host of additional information would be required,up to including,a practical joking teenager,next door,with a home-made EMP device,made from a you-tube instructional.....don't ask...:)
 
I think Sparkychick hit the nail on the head !
Multiple faults !
This would explain why no one can find the problem.
All the testing so far is based around the theory that there is one fault !
When there could be several.
Consider the possibility of several faults !
don't forget to come back and tell us what it was ?
 
Ok very embarrassed as client called another electrician round as I had been busy on an install.
They unplugged the one thing I thought would be fine as it was brand new and fixed in.
Bigger question how does one faulty washer dryer prevent the entires 1st split set of MCBs from switching on the RCCD.
EGO has been hurt a little as some glory hogger stole the spot light, just like the Americans in WW2. Haha
 
How can you do proper fault finding of a scoket circuit with items still plugged in? I don't think you can!

I would say there is still a fault to be found ..............
How can you do proper fault finding of a scoket circuit with items still plugged in? I don't think you can!

I would say there is still

I do. Every RCD tripping fault I come across I want every possible source of the fault left in place when I initially test. Only if L-N tests are being conducted would connected loads need to be isolated.
 
I was reading this thread and was thinking of posting up that you should ask the customer has anything changed recently has any work been carried out etc etc and then got to your post about the brand new washer dryer.

Lesson learned I hope ;o))))
 

Reply to First time in years could not find fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
808
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
940
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
1pm, quite happy doing my planned job. Builder then asks if I could go out to another job where the top lights have all tripped out. I like peace...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock