Search the forum,

Discuss Flashing LED emergencies in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
Hi all changed over some old 2D emergencies 11 in total for LED. They are controlled from some time lag switches on a communal staircase. But as soon as I powered up the lights all flash randomly. Had it before when one has flashed and just changed when to an incandescent but never had them all flashing any ideas anyone. Cant leave them with a disco for long
 
If the time lag switches are pneumatic replace with standard switches and see if that resolves it. I assume the charge indication remains on.
 
Yes the charge light stays on. The time lag switches are touch not pneumatic. It's got me really baffled

Do they have a neutral at the switches?

If they don't then they probably take power from L and S/L by passing a small current through the load to neutral. Far too small a current to cause a normal load to react, but plenty enough to charge capacitors in the LED driver circuits.
Obviously when the capacitors have charged they will then discharge via the LED causing it to flash.
 
Not checked the switches yet tbh so not sure. If that's the case will I get away with changing one fitting back to 2D to stop it

If your contract is to replace them with LED units then no you can't just fit a 2D fitting,plus then you'd have one odd fitting out which doesn't match any of the others creating a maintainence headache.

If the switches are the source of the problem you could replace them for switches which don't cause this, or fit a small resistive load device such as the Danlers 'resloade' or 'resload' for the unenclosed version.
 
If your contract is to replace them with LED units then no you can't just fit a 2D fitting,plus then you'd have one odd fitting out which doesn't match any of the others creating a maintainence headache.

If the switches are the source of the problem you could replace them for switches which don't cause this, or fit a small resistive load device such as the Danlers 'resloade' or 'resload' for the unenclosed version.
Cheers davesparks ordered a load today sure they can live with a couple of flashing lights for a few days.
 

Reply to Flashing LED emergencies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
652
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
603
Afternoon all... The customer has a number of small green lights in the ceiling that are always on. This is a bed and breakfast/hotel. I had...
Replies
6
Views
5K
I have the typical LED on Dimmer switch. All the lights flicker in my house are very inconsistent times. By let me clarify by saying all the...
Replies
0
Views
916
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top