The type of power systems you will encounter in theatrewill be safe (ish) to absolute death traps and because no-one has died theywill be kept !
4 wire (TN-C) is banned by Task Force Power but you willcome across it. Same as TT not allowed but its here.
4&5 (TN-C-S) wire will be the main type but they willbe riddle with N-E bonds fitted randomly in MDP's (Main Distribution Panel's),SDP's (Sub-...) and CDP's. They system will also revert between 4-5-5-4-5-4-...etc producing 'Objectionable' current in EGC (Equipment Grounding Conductors)/CPC's, conduit (pipe). watch out for N bars screwed to the panel with noinsulation (back to a 4wire) and bolted to a metal skinned building.
All new electrical Systems are to be 5wire (TN-S) TFPowerdirective as they are easier to understand and follow.
Transfer switches will be 3pole or 4pole. 3pole T/S areto have only one genny N-E bonded. 4pole, both gennys are to be N-E bonded.
Cable on nearly every distribution system will have beenwhat was around at the time so you'll have 4c rubber in the ground no ductingand about 4-6inch below the hard core. But mostly it will be surface laid evenacross roads with some sand bags on top (if you’re lucky).
Most MCB's will be massively over rated e.g. found a3500A feeding a 120mm 4c SWA other end was a 500A though, so that was better!!!!
Lots of cables will have been given a haircut to get themto fit into breakers, bars, lugs etc
SWA will have been cut with only 10-30% captured andrammed into the earth bar. Split bolt repair is approved.
Earth spike are routinely cut off so a 10foot rod mayonly be 4foot and that’s all a 750KVA genny will have
A cable will start of as a 5c SWA and pop out the groundas a 4c SOOW, so be warned.
120/240V MCB's means they can have 240 3phase in them butcan't be fitted to 230/400v boards but they are.
Boards will be rated to 240V/277V but will have 380-440Vin them.
Ip rating is NEMA. kit should be IP54 min (3R) but isn't.Usual thing is build a cupboard round it.
Guards will be missing in most boards and homemade panelswith live Buss bars open to touch are common.
Gland plates are an optional extra for SWA but as mostSWA isn't glanded off there is no need for them!! So just let the weight of thecable hang from the terminal of the breaker and as there is no gland platethere will be plenty of air to stop the MCB overheating.
Air temp is 50degrees C ground temp is 35 if you botherto do any calc's.
Systems may have been put in for 60Hz 120v kit and todaysgenny is 50Hz220-250v so watch out the amount of kit that gets fried as thewrong voltage is coming out of the socket.
Never come across a frequency converter loads of trannysthough from 50w plug in to 'massive'!

The above are all facts given tongue in cheek.

If you’re here closing down camps buy a solar shower asthere will be no grey water recovery toward the end and LSS units will havegone too. So get use to the idea of dropping a 'Richard the 3rd' in to a bag.

Tony. I never said it was acceptable its what happensthough.
I never said or implied I have a vast knowledge ofanything. But I hope the above helps out someone.

RE = Royal Engineers, so you were part right it doesn'tstand for Real Engineers, but we are :) in every way and every day.

Your right he doesn’t say he is coming out here but I'dsay it was implied as "95% sure I'm got a start on the troop withdrawalcontract" and asking about electrical in Afghanistan. I may be wrongthough on that.

Glennspark, What? You the sites Internetshire enforcer?

no.....
just a fella.....
who got a bit browned off when you gave a very respected member in here a load of verbal diarrhea
 
no.....
just a fella.....
who got a bit browned off when you gave a very respected member in here a load of verbal diarrhea

Loyalty is a good trait and one I admire, but if someone wished upon another that "With any luck you'll take the bullet" I'd be questioning my judgment. I for one say good luck to all our troops in the battle zones and stay safe, keep up the good work and come home soon.
 
OK the bullet was OTT.

From what you say of this ramshackle system it beats me why it isn’t just disabled and abandoned. With the amount of money that’s been wasted over there it would be a drop in the ocean.

I’m sure you could come up with a fun way of disabling the generators.
 
Are you Mad Tony??? That would mean the money wheel would stop spinning and these company's wouldn't get there $4000000000 (yes thats 9 zero's) honey pot!!!! And where you going to put 100000+ troops while its all sorted?

We just keep smiling and repairing trying to make do with the kit that gets delivered*. "We're here to add Band-aids' nothing more" ... "keep it going till the place closes and hope no one get hurt".

*Order 6Amp RCBO type 'B' and get a 40A MCB type 'D'. Cheaper kit from the UAE you see
Order 120mm 4C SWA get 4C rubber (SooW).... whats wrong its got 4 bits of wire in it?!
Order 20mm PVC conduit get 200mm Drain pipe, with 15000 20mm saddles (ordered 150 (3boxes))
Order E/M light for 230V 50Hz get 120v 60Hz or.... 277v 60Hz (frequency is still out)

This morning found this 4C SWA with SWA cut off below board, neutral then linked to Earth bar with a metal bar (looks like a dinner knife handle) with the EC wrapped round that leading to a cut down ground rod !!

Get caught sabotaging kit you'll end up in a military nick in the states for a couple of years playing hide the sausage if your lucky, unlucky you'll be playing hide the coke can sized sausage for a couple of years :eek:mg_smile: !!
 
OK does this make sense, as each camp is abandoned destroy the machines and infrastructure. (From you’re description, is there anything worth saving?) No personnel need stay back.

The troops and ancillary personnel will have to be dealt with somehow no matter what.

As you say, there’s money to be made. The trouble is, it’s tax payers money.

The main thing I will disagree with you is you’re statement “boots on the ground”, inexperienced personnel are so dangerous!
 
Some Genny's will be kept and moved about, trouble is Afg is landlocked, so no way of getting the kit out.

Pakistan open's and close's the boarder all the time so kit struggles to get in/out, so whats not expensive/easy to move will be destroyed. Test meters which arn't used in the States are driven over, seen 20+ Flukes crushed under a truck wheel in the name of accountability and to stop them falling into the Enemy's hands !!! What Terry wants with a Fluke? I don't know, I'd be more scared of Terry running at me with an AK then a Fluke on Insulation Resistance test !!

Some places will be destroyed totally (nothing left) and the area ploughed to even get the power cables up, some will have brick building left behind for Afg Army etc to use and some places are being specially built for the Afg (Garrison sized) filled with everything you could ever dream of.

What else you going to do with the money Tony... Health, education etc? Best keep throwing another bundle on the fire to keep me off the streets of the UK.

Inexperienced people are a danger but what would you prefer: an inexperienced electrician working on the electrics or (I KID YOU NOT) a soup chef from a hotel in Dubai playing with it!!? They're paid the same and the company skims the top off. The wheel keeps on rolling.
 
Crazy, crazy world.

We had plants demolished. I asked can I get --- out first? No it’s all going, it’s all salvage for the demolition company.
Two weeks later I’m putting an order in for something that’s just driven past me on the back of a scrap wagon.

Correction to the above, stupid, stupid world! (Corrected for accountancy).
 

Reply to Floating earth - generators in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I've recently had 2 customers enquire about installing a backup generator for their domestic premises. After a lot of research...
Replies
17
Views
3K
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K
Hi all, I've got a small catering business out of a converted horse trailer and purchased an inverter generator to power the trailer, mainly just...
Replies
8
Views
6K
For emergency use, when there's a power outage, the current situation (no pun intended) is that I'm running a hook up cable from the 16A socket on...
Replies
3
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock