Search for tools and product advice,

Discuss Found during fault finding in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
16
Hi guys just wanted to ask if there are any Irish electricians here that can tell me whether these examples of making off SWA are accepted in Ireland.
Just had to fault find a light not working in a garden and opened up a couple of manholes to find PVC 4x4 waterproof boxes with SWA going into them through PVC glands with 90% of the outer core cut away the remaining steel connected to the earth of the multi core inner cable.
This was wired by an Irish company for a customer in Scotland.
I spoke to the electrician that wired it and he was of the opinion that that is the way they work in Ireland and the niceic are ok with it.
Some feedback would be appreciated.
Thanks

IMG_20190902_144135.jpg

IMG_20190902_145746.jpgIMG_20190902_144636.jpg

IMG_20190902_142839.jpg
[automerge]1567516983[/automerge]
Blue gel is to make the boxes waterproof but not all the boxes had it and some had less than half filled.
I never put the gel in it was the other electricians
 
This was wired by an Irish company for a customer in Scotland.
I spoke to the electrician that wired it and he was of the opinion that that is the way they work in Ireland and the niceic are ok with it.
Some feedback would be appreciated.
Thanks

It doesn't matter whether it's the way they work in Ireland, they're working in Scotland so need to comply with regs and good practice appropriate there.
 
That is just horrible
Lazy
Not up to standards
If that’s the way he does it in Ireland it is still wrong, England, Scotland, Ireland and Timbuktu it is still WRONG.

I am certain there are loads of good Irish electricians, but he is not one of them

In my humble opinion.
 
I doubt the NICEIC would be happy with it as it more than likely goes against manufacturers instructions. Can you guarantee those strands of SWA would carry the fault current for the duration of the fault? Also using magic gel to get around crap workmanship is just ****.
 
There is only 1 way to terminate SWA and that is the correct way using Industry standard glands and enclosures the ness you have shown is NOT the correct way the "Electrician" has reduced the size of the Armour to allow him to terminate the remaining strands of Steel into a normal connector, not the correct way to do it, are you sure he was actually an Electrician, cuz if he worked for me I would sack the villain, Oh and I'm not Irish either.
 
No that method is not acceptable, I've seen different variations on that theme with some people bringing a few strands through a normal SWA gland, they are all incorrect.
[automerge]1567533292[/automerge]
There is only 1 way to terminate SWA and that is the correct way using Industry standard glands

That's not strictly true, there are different types of glands and methods of terminating SWA. Apart from the standard glands there are various hazardous area glands, top hat glands for the larger sizes or specialist lamppost glands. Then there's range of heatshrink based terminations for specialist applications andof course cast resin terminations.
 
Last edited:
It doesn't matter whether it's the way they work in Ireland, they're working in Scotland so need to comply with regs and good practice appropriate there.
I can assure that’s not the way it’s done in either the Northern Ireland or the Republic of Ireland.
That is just horrible
Lazy
Not up to standards
If that’s the way he does it in Ireland it is still wrong, England, Scotland, Ireland and Timbuktu it is still WRONG.

I am certain there are loads of good Irish electricians, but he is not one of them

In my humble opinion.
It’s a bodge and that’s that. It would not be acceptable in any part of Ireland.
 
It's not allowed in Ireland.

I'm registered with both RECI and the NICEIC and neither of them would accept or tolerate this. RECI (the Irish Regulatory Body) would record a breach of the Wiring Rules if they came across this during an inspection, and the contractor would be made to rectify it and provide evidence of the rectification (or have an additional inspection at cost to them at RECI's discretion).
 
Maybe they are getting confused with split concentric?

On another note what's with the insulation colours in that SWA? How long has it been available with brown, blue and G/Y and does that actually comply with the British standard?
 
Maybe they are getting confused with split concentric?

On another note what's with the insulation colours in that SWA? How long has it been available with brown, blue and G/Y and does that actually comply with the British standard?
It's common to have those colours in the south of Ireland.

What you need to remember is that remarking conductors of different colours is a prohibited practice under the ETCI National Rules for Electrical Installations. So three core SWAs are available in single phase colours. (From memory it needs to be 7-core or more to be allowed to remark the conductors.)
 
No that method is not acceptable, I've seen different variations on that theme with some people bringing a few strands through a normal SWA gland, they are all incorrect.
[automerge]1567533292[/automerge]


That's not strictly true, there are different types of glands and methods of terminating SWA. Apart from the standard glands there are various hazardous area glands, top hat glands for the larger sizes or specialist lamppost glands. Then there's range of heatshrink based terminations for specialist applications andof course cast resin terminations.
do you have links for these other glands? i have seen the tophat style before but for 33kV i believe. the others ones when i searched didnt really show me much more than standard gland packs.
 
On another note what's with the insulation colours in that SWA? How long has it been available with brown, blue and G/Y and does that actually comply with the British standard?
Had some of that on a job a few years ago, the customer specced it so we had to source it from our suppliers, TBH it did cost a few quid more as not many people use it. Still standard SWA with the relevant BS number.
 
It's common to have those colours in the south of Ireland.

What you need to remember is that remarking conductors of different colours is a prohibited practice under the ETCI National Rules for Electrical Installations. So three core SWAs are available in single phase colours.

That must get pretty annoying then, do you have to order specific combinations of core colours to suit every cable run? If you need to run L, S/L, N and E do you have to use cable with two browns in it?

How do you deal with multicore cables for controls or multiple circuits? For example where its not possible to install conduit/trunking I use 12 core SWA to take 6 circuits to a standard stage lighting bar, 19 core for a 8 circuits etc, would this not be allowed and you have to run seperate cables?
 
That must get pretty annoying then, do you have to order specific combinations of core colours to suit every cable run? If you need to run L, S/L, N and E do you have to use cable with two browns in it?

How do you deal with multicore cables for controls or multiple circuits? For example where its not possible to install conduit/trunking I use 12 core SWA to take 6 circuits to a standard stage lighting bar, 19 core for a 8 circuits etc, would this not be allowed and you have to run seperate cables?
As for your first question you could use brown, black, blue and green/yellow, with heatshrink sleeving on the black (assuming this is on L1 or L of a single phase supply) of brown.

As mentioned RE: 12 core SWA etc. that cables of 7 cores and greater are exempted from this Rule.
 
Another cable always used in Ireland is pvc/pvc twin brown for switch drops and strappers etc. rather than using a T&E and sleeving the blue. I’ve never really understood why it is not readily available in mainland GB.
 
do you have links for these other glands? i have seen the tophat style before but for 33kV i believe. the others ones when i searched didnt really show me much more than standard gland packs.

Top hat glands will be supplied with some switchgear for the biggest sizes of cables.

Various street lighting equipment is available, such as this cutout
normal_GBH-Street-Lighting-Cut-Out.jpg
 
Another cable always used in Ireland is pvc/pvc twin brown for switch drops and strappers etc. rather than using a T&E and sleeving the blue. I’ve never really understood why it is not readily available in mainland GB.
what do your use for 3 core and earth? ie unswitched, switched and neutral
[automerge]1567542370[/automerge]
Top hat glands will be supplied with some switchgear for the biggest sizes of cables.

Various street lighting equipment is available, such as this cutout
View attachment 51872
ah, so the ones for lamppost cutouts are just smaller top hats?
 
Another cable always used in Ireland is pvc/pvc twin brown for switch drops and strappers etc. rather than using a T&E and sleeving the blue. I’ve never really understood why it is not readily available in mainland GB.

I have heard that comment made quite a few times over the years
Not sure if there may be a regional aspect to its availability :confused:,though I doubt it very much

I personally have installed thousands of metres of twin brown over the years,I have never found a problem sourcing it locally
Its been the minority of occasions when I have used Brown/Blue with over sleeving and never because Brown/Brown was not available
 

Reply to Found during fault finding in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K
Hi all! This is my first post and I have registered to ask for some help with troubleshooting an electric shock I got from a plastic light switch...
Replies
44
Views
8K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock