Lads show me where it states that Richards left hand scenario is acceptable and conforms to 7671Some socket outlets state on the back max 4x2.5mm (yes not all, but some)
The pic on the left is perfectly acceptable. How would you feel about the pic on the right with a 4mm to the first spured socket & 2.5mm to the next one?
No problem, you are entirely entitled to disagree, and from a practical point of view I would not want to do it.So your saying that providing you take two spurs from the same socket it's OK? Sorry disagree with you on that one
BS7671 does not give you the option of spurring from a spur without fusing down, however you could design it that way as a departure from BS7671, but again you would risk overloading the ring at the take off point and would be able to pull over the current carrying capacity of the 4mm from two double sockets, so would have to take diversity into account for the socket outlets which is hard to do (though obviously applied for general socket circuits in a very large way).Some socket outlets state on the back max 4x2.5mm (yes not all, but some)
The pic on the left is perfectly acceptable. How would you feel about the pic on the right with a 4mm to the first spured socket & 2.5mm to the next one?
Lads show me where it states that Richards left hand scenario is acceptable and conforms to 7671
This is not specifically prohibited by BS7671 therefore it is permitted.Lads show me where it states that Richards left hand scenario is acceptable and conforms to 7671
Lads show me where it states that Richards left hand scenario is acceptable and conforms to 7671
I'd be amazed if the whole circuit conformed to any standard. Especially the light supply fed around the switch by splitting the outer insulation, and the way the cable had been fed into the backbox was a joke.
Seems there is a difference of opinion as to whether two spurs in parallel is acceptable and two in series also. But as I had two in parallel and one in series plus a light spur off the same ring point I'm hoping we can agree it was a proper lash up!
Thanks very much for all the comments
Well you can tell the spark that only does posh houses, security lights, trouser presses. What next a teasmaid!I see this alot. Its always the single gang socket on the landing that gets the kicking.
I bet one of the spurs feeds a security light, and the other is for a trouser press in the wardrobe that backs onto the single socket :laugh:
Personally, I'd be looking to change that arrangement, not because of some reg on spurs which may or may not exist, but simply as I'd be concerned about the mechanics of four conductors jammed into a single small terminal and not actually being that secure.....and there ARE regs for that one!!
[QUOTE
If you endorse that point of view then there should be a regulation against 10mm cables in shower pullswitches.
[QUOTE
Personally, I'd be looking to change that arrangement, not because of some reg on spurs which may or may not exist, but simply as I'd be concerned about the mechanics of four conductors jammed into a single small terminal and not actually being that secure.....and there ARE regs for that one!!
it's not just the terminals, it's the conductors squashed in the backbox that's also a major concern.