While i am on could i send out a big thank you to Sedgy34 for PM to give me his mobile number and helped with testing of solar for my EICR. Top Man!
No name on it anywhere! That's a surprise! Have informed the owners and they are going to get in touch with firm.
OMG!! where to start!!
connection at the CU is just wrong, too much to list. Penetration through roof felt, not part of your check but it looks like they have just punched a hole through the felt, lazy breech of the regs, they shoiuld have come through the overlap, bet there's no protection for the cables rubbing on tiles either. All that cabling hanging out the bottom of the meter is against regs as it's only single insulated. We use a jewis box under the meter to do earth connection and house stripped cable.
All cables need to be clipped in place and then cut to length.
labels need to be in place on isolators and inverter but also along the DC cable to show it's DC not coax.
there's probably more but thats all I dare look at at the moment for fear of my heart!
One of the shabiest jobs I've seen!
HEY TC are you able to find out who were the installers are of this, im sure theres quite a few on here now intrigued about this company after seeing that.
Hi sedgy, i will find out if i can but as you know its a big organisation that own this house and a lot of properties (don't want to say on the forum).
Not sure to post name of solar company if i find out name, lynching mobs were outlawed years ago!
that spaghetti looks like coax.
And this is the problem, I do not know telectrix, but judging by his posts he is a good electrician and he thinks it looks like coax, so what would joe public make of this? oh it is just old coax, snip, maybe 700v DC that is going to hurt...
As installs go, this is about as bad as you will get, nothing is labeled, connected to supply wrong, all the cables are a mess, (Tower will not get rich from these guys)
The surprising thing is it is working, did anyone notice how much lower the generation meter is to the inverter reading?
Well TC you have your work cut out there...
Utterly pathetic. We all make mistakes but this whole install shows an utter lack of effort.
I've said it before and I'll say it again - I'll bet their QMS is top-notch.
It'd class as a dangerous installation in my book, so IMO you're actually obliged to sort it out, being the last electrician in.Trouble is, is that i work for a builder that reports to a surveyor that reports to the owners! Have been told that they will get in touch with the installers but they are the sort of people that will just say "oh you just sort it out"!
Now i know a little less than SFAll about solar, but i know how to clip cables! If i get the job i may be back on here asking for advice! Mind you i don't know how i would come off if i touched it? Got to be a minefield out there if you mess with it and you are not registered. Any thoughts on that?:thinking:
you don't need MCS though to be allowed legally to work on solar, only Part P if it's in a house.Put it on your eicr inform who you have too then wash your hands of it.
I have masses of solar experience having worked as an installations manager round the country have all the quals you can get but I still dont touch solar in the field now as I am no longer in the industry and hence have no Mcs.
you don't need MCS though to be allowed legally to work on solar, only Part P if it's in a house.
MCS is only for claiming the feed in tariff.
No that is supply authority meter.Just a thought ... if that meter is actually the landlords, installed as a sub-meter after the suppliers, and the landlord is billing the tenant, it could be in the right place...
Been struggling with this for a while Tel, have changed those two C2's to C3's backwards and forwards. My reasoning for C2 is with no labeling someone could remove main fuse (God forbid) and the D/B is still live so potentially dangerous. Also cables in loft could be tripped over or cut so potentially dangerous.i might be inclined to downgrade your C2's to C3's as although rough, i can't see a potential danger.
looks to me like it's got an RCD in the garage unit.Do you need to mention that the PV has no RCD,
PV has got RCD protection, main fuse to 63A RCD, 20A breaker see pictures. Unless you mean up in the roof space?Do you need to mention that the PV has no RCD, and being a TT system it is usually a requirement?
Just for advice, if there is no AC supply to the inverter then there would be no AC coming from PV system, an inverter can take 5 seconds to shut down though, hence why they should never be on a 'shared RCD', but the DC would still be live, well in the daytime of course...
looks to me like it's got an RCD in the garage unit.
looks about right TC, and now I've seen the photos I realise what you meant by connected at the suppliers fuse, not quite as bad as I'd pictured it (I'd been imagining 2 sets of tails somehow wedged in to the same hole).
bit of a dogs dinner, and the customer is definitely loosing out on the free leccy (which if it was rent a roof, then that is the only benefit they've be getting from the system, so just a bit important), but I think you've got the levels about right, though I agree that the C2s probably are borderline between 2&3.
here's one I did earlier!View attachment 12609 Not the best I've ever done but the only photie I've got to hand.
labels went on later before anyone comments!
Middle set of tails go to dedicated CU. Right hand tails (as we look at it) go to main CU
HEY TC,
good pic! tails are undersized for 100amp suppliers fuse
All looks like cheap tat as well, probably won't last more than a few years!
Think that's the roughest solar electrical install i've seen, I wonder what the roof work is like...
Moggy, make sure you don't strip the outer sheath of the tails outside of the henley block otherwise you have a single insulated conductor with no mechanical protection outside of an enclosure which would warrant a defect code on an EICR.
It's always been the case that you can't have a single insulated conductor outside of an enclosure or containment but you're right, there's many installs out there with that issue and the DNO are more guilty than most, especially with their meter terminations. Maybe that's where the habit has come from?
If you're carrying out an EICR then just report and code them appropriately. No need to make any changes there and then, only if the customer chooses to have the defects rectified though the meter terminations are obviously the DNO's responsibility. You can still note them on your EICR though.
I think tails are undersized for 100 amp suppliers fuse
If the RCD short circuited then the prospective fault current could be thousands of Amps.If there's a 20A MCB in the 2 way CU then how can the tails be subjected to an overload greater than the rating of the MCB?
In other words, the MCB is your overload protection and the tails are fine.
Think of an 800A busbar chamber with a few 32A switch fuse isolators fed from it. Would you expect conductors rated at 800A to be terminated into the 32A switch fuse?