Hi all I’m in the process of upgrading my solar set up to 2x 260w panels with a 40a mppt tracer
I’ve just bought a 2000w(4000w peak) inverter which will be running off my 2 120ah leisure batteries connected in parallel using 70mm2 cable fused at 350a
But my question should the fuse between the batteries also need to be 350a
Thanks all
 
The batteries are in parallel
I took the wattage of the inverter and made my calculations
4000w/12v= 333.33amp
According to the site I got the cable from
PVC70 888/0.30 70 485 15.5 Black, Red
It can carry 485a
So my thoughts were the inverter is internally fused so just had to protect the cable what size fuses would you recommend then to go from
1, battery bank to inverter
2, in between the 2 batteries connected in parallel
 
that cable is, as you say, capable of 485A. it's not a type that we use generally, so our bible does not list it. however, your batteries will last about 30 minutes running at that. if batteries are in parallel, you need a fuse in the +ve going out to the inverter. no need for additional fusing on the battery side as the 350A fuse will blow under overload/short circuit.

you also need to calculate the load on the inverter. that's what will determine your battery current, not the max. load the inverter will supply.
 
So what if there was a problem in one or both of the batteries you recommend not having a fuse between the 2? For my peace of mind in case there was a problem (dead short etc) I would rather have protection between the 2 and not risk damaging both and/or the wiring there will be a fuse between the batterie bank to the inverter as stated in my original question there will be a fuse between the batteries my question is should it be the same size as the one going to the inverter
Thanks all
 
can't see any reason for a fuse between the batteries. how can a + to a + short unless the batteries are in a metal enclosure and trhe insulation of the link cable wears through and shorts on the metal enclosure.
 
So you can’t see that a dead short on one battery couldn’t damage the second battery by using the cable to transfer the short if there was a fuse in between it would blow thus protecting the second battery and the cable? Or am I really missing something here?
 
The extra fuse would protect either battery from a dead short on the other.
Thing you gotta ask, is why would you have a dead short on one of the batteries.
Do you run around dropping metal objects across the battery terminals much?
 
The extra fuse would protect either battery from a dead short on the other.
Thing you gotta ask, is why would you have a dead short on one of the batteries.
Do you run around dropping metal objects across the battery terminals much?
Why have an rcb then do you do installs expecting things to break
It’s there for safety in case the unexpected happens
 
Why have an rcb then do you do installs expecting things to break
It’s there for safety in case the unexpected happens
RCDs are primarily used in case someone plugs in a defective appliance, drills though a cable concealed in a wall or to add an extra bit of safety for someone having a bath or taking a shower.
Your proposal is to protect the batteries against a metal object either falling or deliberately being placed across the terminals of the other battery.
With vehicle batteries, the common practice is to place a piece of plastic across the live terminal or to use a rubber boot over the connector.
 
RCDs are primarily used in case someone plugs in a defective appliance, drills though a cable concealed in a wall or to add an extra bit of safety for someone having a bath or taking a shower.
Your proposal is to protect the batteries against a metal object either falling or deliberately being placed across the terminals of the other battery.
With vehicle batteries, the common practice is to place a piece of plastic across the live terminal or to use a rubber boot over the connector.
Ok well thanks for the advice but after gathering information from a dedicated solar forum I’ve found that not only is it recommend but in some countries it’s law so the fuse will be fitted as would rather be safe than sorry and I’m not one to cut corners even though it’s highly unlikely it can still happen
 

Reply to Fuse between batteries in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, So I purchased a Novopal 2000w/4000w(Peak) Pure Sine Wave Inverter DC 12V to 110V/120V. I purchased this so I can hook it up directly to...
Replies
5
Views
591
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
697
Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
Hi, My camper has a new 12v battery and I have wired up a split charge relay with a 100 amp blade fuse near van battery and a 100 amp blade fuse...
Replies
7
Views
2K
Hi All, I'm moving into telecoms and looking for some help on disconnecting battery strings. I come from a domestic background so have not got...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock