Discuss Fuse Constantly Tripping in the UK Electrical Forum area at ElectriciansForums.net

At least they didn't do what one spark did to a friend of mine :mad:namely told the customer they had a "faulty Earth" :mad::eek: and promptly disconnected it (CPCs) from a S/O :mad:, I got involved later when instead of the RCD (split load board) tripping the fault resulted in the MCB tripping as one of the legs of the RFC started burning up, they still charged my mate for half a day without even narrowing down the fault :(, some people shouldn't be let loose.
 
If the RCD never trips with the kitchen sockets off then most probably a live-earth fault somewhere on that circuit.

Water could be the cause, do you have any external sockets, or perhaps lights fed via a fused connection unit? Leaky washing machine or dishwasher? Turn all isolators off for appliances in the kitchen, check cupboards for appliance sockets etc.

If none of that comes up trumps then I'm afraid you would need to get someone else in to test it. Were you at home when the other electrician came? What did he actually do and what did he tell you when he asked for payment?

Unfortunately it didn't happen while he was here so none if his tests showed anything up. He had a little beepy thing that he plugged in to various sockets which showed no faults and he mentioned testing something to do with the fuse box which also showed no faults.

He checked about outside lights but they are on other RCD, and disconnected some external plugs as he thought that could possibly be the problem.

Just unlucky that it tripped about 5 times before he arrived and 10 mins after he left but not while he was here.

It is v intermittent though. We woke up to it tripped on Saturday morning, turned it back on, it went again once, then was fine until waking up this morning. Sometimes it has been an hour or so in between, sometimes immediate.
 
Old fridge or freezer with a failing compressor?
 
Please help!

A fuse keeps tripping over and over again. I have 100% narrowed it down to being on the "kitchen sockets" circuit and definitely not to do with overloading or any particular appliance being used.

Believe me, I have unplugged everything in the entire house and it still goes, had one thing plugged in at a time and it still goes, etc. It is not down to one particular socket or thing that's plugged in.

It started randomly in the middle of the night, we discovered it when we woke up. We have not done anything differently recently, nothing new plugged in, no new screws or nails put in walls.

What else could it be please and is it something I can fix myself / if not, will it be a quick/cheap job for an electrician to figure out and complete. I've already wasted £140 today on an electrician who did absolutely nothing.
Firstly I concur with the others this person who ripped you off was certainly not an Electrician, or if he was he needs to give up charging people for his work, a disgraceful outcome from a so called professional.
Did he do any testing with meters etc, sorry to sound negative, but it pees me off no end when some Muppet turns up has a look around, charges the earth and does a runner, certainly hope a forum member close by will be able to help you out, please let us know how you get on, oh one more thing, was this person recommended to you, and can you recall if he was a member of one of the Competent Persons Schemes (NICEIC, NAPIT, STROMA, or any of the others) anyhow good luck. If so you may get some recourse if he is a member of a CPS, by complaining to them, Trading standards is another route for you yo try.
 

Reply to Fuse Constantly Tripping in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock