Is it acceptable to leave a 2 core 10mm2 MICC cable supplying an upstairs flat on a 100A suppliers fuse? (Maxing demand is acceptable and disconnection times are within tolerance.)
 
No, existing installation. Just wondering when there is no space in the meter box for a switch fuse. I come across this every so often when carrying out periodics.
 
NO. Without fusing down, you would exceed 3m which the supplier will say is the max unfused.

Also regs say max of 3m back fusing.
 
Last edited:
Is the pyro the property of the DNO. I know around here many flats were serviced by DNO in pyro. I have had faults on these on occasions and DNO changed them for hybrid concentric.
 

Reply to Fuse Downgrading in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
1K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
My customer has had a completely new supply installed to his garage. The DNO has not put a fuse in the cut out though. I'm guessing he needs to...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock