Lizlimpet

DIY
Reaction score
2
Hi All, and thanks in advance for reading my question. I have soent the last 30 mins searching online without an answer to y question.

My kitchen is currently being rewired. The hob is going to run off a fused switched spur. The switched spur is currently wired directly into the kitchen ring so that it up has the ring going through it and then the spur to the hob plug coming off it (so three wires). Am i right in thinking that both wires of the ring (the "in" and the "out") go through the suply side and the single wire to the hob plug come off the load?

Is it ok to do that and would it pass an electrical test ?

TIA20200305_115936.jpg
 
Last edited by a moderator:
Hi - yes and maybe - but if you don’t mind me asking - have you got the hob already? What make and model is it? If you’re having the kitchen rewired I’d consider putting in a new circuit rather than taking it off the kitchen ring final circuit.
 
Thanks for the reply.

No I haven't got the hob already, but it will be a basic one.

So just so I understand, if adding the fused spur to the ring you keep both sides of the ring on the supply?

Thanks
 
Thanks for the reply.

No I haven't got the hob already, but it will be a basic one.

So just so I understand, if adding the fused spur to the ring you keep both sides of the ring on the supply?

Thanks
Hi Liz,
Are you doing the work yourself?
I expect they do make 13A hobs although I cant remember having come across one.
It sounds like you just want some basic information on how to do it which makes me think your mind is made up and you are going to fit it whatever. However, do be aware that hobs generally use lots of power (more than an oven) and I have only ever fitted them on their own supply.
Could you give the make and model?
Thanks.
 
Hi!
Apologies, I should have clarified - it will be a gas hob so will just need power for the pizo (sp??).

Does that change your answer?

Thanks
 
Hi!
Apologies, I should have clarified - it will be a gas hob so will just need power for the pizo (sp??).

Does that change your answer?

Thanks
That makes quite a difference Liz :D .
I tend not to give specific DIY advice so all I'll say is it's fine for a gas ignition to be run from a fused connection unit assuming the ring is in a safe condition.
The difference between you doing it and an electrician is that before adding anything to the ring the electrician would test the continuity of the ring and also the earthing amongst other things to make sure it is safe to be added to. For the sake of £50 it would be worth getting an electrician in just to test it, although they would probably be able to make the connection as well for that price if all the cables and boxes are in place. You would then know for sure that it was all safe rather than just hoping it was.
 
Your gas hob may come with a plug on it for the igniter. So your sw/f would end up being a single sw socket
 
  • Like
Reactions: DPG
Thanks, that's what I've put in! Great to get the reassurance!

Sparky coming tomorrow to test everything:)
 

Reply to Fused spur on ring main in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
473
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi, In the example pic, if the double socket was already a single spur off a socket in the ring main, as I understand you can only have a single...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock