I need to spur off a ring main to two locations a Boiler Control and Downflow heater.

Is there anything wrong with installing one 13A fused spur unit adjacent to a socket on the ring main and running both cables out the back of it to seperate fused spur units in the appropriate locations?
 
the only downside i can see is that you''ll probably have a 13A fuse for the heater and thus have no discrimination with the 1st FCU .
 
In the end I extended the ring (customer got a free socket on the other side of the wall!) and ran two seperate spurs as the downflow heater needed a 13A fuse so discrimination would have reared its ugly head.
 

Reply to Fused Spur Query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
472
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
614
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock