Discuss G4 LED stay on after Dimmer is Switched Off in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
The G4 110V 3W dimmable bulbs I purchased work with a dimmer. I can brighten them and dim them, but when I turn the dimmer off, the LED bulbs remain on (the same level as the lowest brightness). I am using a Lutron Maestro LED+ Dimmer. This style dimmer has tiny lights built into the switch so it can be found in the dark and I can see the degree of brightness. In series, could the switch be leaking current to the LEDs? Thanks.
 
Last edited:
n series, could the switch be leaking current to the LEDs?

Yes. Most 2-wire dimmers other than traditional types with a physical switch that clicks off, pass a small current through the lamp all the time. Yours with the locator lights might need more current still. It will have a minimum lamp wattage with which it is designed to work but this type of effect is quite common with any LED fixture.

One possible solution is to bypass the LEDs with a snubber network (combined capacitor and resistor) that will allow the dimmer's standby current through. Some experimentation might be needed. Alternatively, changing one LED bulb to a tungsten equivalent (if the fitting allows for tungsten) will work. Other than that, the dimmer would need to be changed to a type that uses a neutral connection (if there is a neutral at the switch location) or one that does not require current in standby.
 

Reply to G4 LED stay on after Dimmer is Switched Off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I fitted a dimmer switch by daisy chaining the dimmer switch to a normal plug. The challenge is the light flickers at random intervals. If I take...
Replies
3
Views
241
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
I have a led panel that i want to dim. It is dimmable but without a dimmable driver. I have a dimmer module and a dimmer switch as shown in the...
Replies
0
Views
541
our dimmer switch stopped working after 7 years so went to replace it at the weekend. When I opened it up, the black wire was in the common slot...
Replies
0
Views
221
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
674

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock