Good evening everyone

Can any help or give me some advice please on measuring bending galv conduit.

My question is bending long 3m lengths.
Say for example you need to bend a full length. 400 mm to back of bend. If you insert measured end first into the former obviously you can bend it to 90 degree due to length!
If I do it upside down the long length hits the ceiling if you insert measured end in first!

Hope this makes sense but can anyone explain how you bend this example please? Surely there must be a way of measuring by inserting opposite end into former first?

Many thanks
 
Get a bit of scrap conduit, mark it at 400mm, put it in the bender with the mark lined up with the back of the former and the 400mm sticking forwards.
Pull a 90 degree bend in it and then accurately measure the distance from the back of the bend to the end of the conduit.
Subtract this new measurement from your original 400mm and that is the amount you need to add on to the 400mm to get the bend you want.
 
Get a bit of scrap conduit, mark it at 400mm, put it in the bender with the mark lined up with the back of the former and the 400mm sticking forwards.
Pull a 90 degree bend in it and then accurately measure the distance from the back of the bend to the end of the conduit.
Subtract this new measurement from your original 400mm and that is the amount you need to add on to the 400mm to get the bend you want.
Hi Dave thanks for this. Sorry for stupid question but assume you mean the measured point from goes into former first?
 
If you mean the conduits hitting the floor before it reaches a right angle then make the bend by pulling the bar up, instead of down. If it hits the ceiling find a room with a higher ceiling. One thing to remember with conduit is it's all about the angle of the dangle; remember that and you cant go far wrong !
 
As Davesparks says find an off cut and mark it 400mm from one end; line up this mark to any reference point on the former (can be the back of the former or simply a mark on the former; it doesn't matter where as this is just a reference point aka datum point). Pull the bend, take it out and measure from back of bend to end of conduit. Its unlikely it will be 400mm; however this measurement will determine how much you need to add or subtract from the 400 mark to obtain your desired measurement. So, with this is mind, on the conduit you wish to fabricate, mark 400 from the end, plus or minus the measurement determined on the scrap piece, align this new mark with the datum point and pull the bend. Its should be 400 to back of bend in this instance. A bit long winded explanation but that's about it.
 

Reply to Galv conduit help please in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I’m an electrician trainee and very new to conduit bending. So the length of the floating wood is 9 1/2” and the height is 10 3/4” I’m doing a...
Replies
2
Views
919
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
Replies
1
Views
4K
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock