Currently reading:
Garden lights feed

Discuss Garden lights feed in the UK Electrical Forum area at ElectriciansForums.net

T

tears200

Guys im in need of your help and guidance again please. Im a spark in a industrial environment so when I get asked to do any residential jobs sometimes I get stumped. What it is is my pal has asked me to put him some outside lights in his back garden, the builder has ran and buried a cable in the soil from one end of the garden to the other, one end of the SWA pops up in the soil im going to put a IP 65 rated socket with RCD on the end. But im stuck with the other end. It comes up directly beneath a twin IP 65 rated socket with RCD, this would be great if I could put a 3 pin plug on the SWA but I cant also theres no real space for me to put a metal box to terminate the SWA in due to downspouts being in the way, the only thing I can think of is to drill a hole through to inside feed the SWA through and terminate inside then feed a flex back outside. Does anyone else have any ideas as im stumped. Thank you again for taking the time to read this and I look forward to your reply.
 
i meant a non IP rated FCU. and yes it will be easier to gland the SWA into an adaptable box. fit banjo or earthing nut/s.
 
Oh yes im with you thank you, you've been a great help. That's the way ill do it just got to tell my mates wife that she will lose her 2 gang socket. Wont go down well she a dragon. I will blame you. ha ha Thanks
 
Once you have the FCU in place then you can move the existing socket to a nearby location and feed it from the FCU as well as feeding the cable to the far end.
If you use a plastic box you just need to ensure you maintain the earthing through the box. Also use a piranha nut as some boxes are a bit thick to get the gland nut on with the banjo.
 

Reply to Garden lights feed in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top