Discuss Garden workshops/Shed supplies in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi All,

I’m looking for a bit of advice with regards to a clients outdoor workshops.

Would the diagram attached be a acceptable method of installation? One supply from the house into a DB (RCD protected Garage unit) in the first workshop then a supply from there into the second workshop with DB and both with a TT earthing system (DNO is TNC-S supply)
 

Attachments

  • DB5C88B7-E6D3-4E8B-BBE6-655735DA2945.jpeg
    209 KB · Views: 27
Welcome to the forum mate.
Boring bit first before the question. This work falls under Part P and is notifiable.

What earthing arrangement is your house supply?
Why TT the supplies to the garage and workshop 2?
What's the length of runs?
So you have a 25A breaker in DB1 that will feed DB2. What size breaker are you using in DB2 to feed DB3?
 
Cheers Spoon ?

The House supply is TNC-S and I would be looking to upgrade the current breaker in DB1 to a 32amp supplying DB2 then 0ver to DB3 with a 20amp.

DB2 is 5mtrs away from DB1 and DB3 is 7mtrs away from DB2.

I hope that all makes sense
 
Cheers Spoon ?

The House supply is TNC-S and I would be looking to upgrade the current breaker in DB1 to a 32amp supplying DB2 then 0ver to DB3 with a 20amp.

DB2 is 5mtrs away from DB1 and DB3 is 7mtrs away from DB2.

I hope that all makes sense

Curious at to why TT the buildings?
I take it that there are no extraneous conductive parts in either building?
 
Curious at to why TT the buildings?
I take it that there are no extraneous conductive parts in either building?
I didn’t see any in either of the buildings and I did check for pipe work etc from the house entering them. I was thinking more of the DNO supply being PME and if a break in the Neutral/Earth was to occur…..but I guess I’m over thinking that.
 
.but I guess I’m over thinking that.

you are. lost N is very rare, could be a problem if outbuildings are made of metal, otherwise, us the existing earthing system. the low Zs values outweigh the risk of lost PEN.
 
You'd be keeping each of the 3 boards rcd protection independent of the other boards

You don't want any fault in one building tripping RCDs in another , basic sensible design
 
6mm 3 core?

If you are intending on making the outbuildings TT then why not use 2 core?

with the cost difference, you could then run 2 x supplies from db 1 and supply each building with its own breaker.
 
If they are to be used as workshops I would also suggest some emergency lighting in case power fails for any reason. The sealed LED baton style lights are often available with emergency battery back-up built in.
 

Reply to Garden workshops/Shed supplies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
752
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock