Hi Guys,
I'm looking for some opinions, I've got a customer with a gas meter in an in ground box (see picture). The pipe to the meter is plastic as the meter was moved a few years ago but its metal where it enters the house from the outgoing side of the meter.
Would you bond this?
20211204_131625.jpg
The customer doesn't want the disruption as there is a bathroom between and a semi solid floor
 
If there's a metal pipe leaving the house, however short, it needs bonding.
If there's a problem easily getting a bond there then I'd rather see bonding to the gas somewhere that nowhere, and there is a clause in the regs that says "as near as practicable to the point of entry".
I've seen bonding run a long way around the outside of a property too, it doesn't have to take the shortest path.
So maybe having a good hunt for the easiest place to get a bond on it is the way forwards. A common possibility is extending the bond (appropriately) from where the water is bonded on to the gas intake of the boiler.
 
Why?
For what reason?
The fact it's you that are asking already means I'm wrong ;-) And maybe the statement was too vague.
But I'd have said it's an extraneous conductive part, 411.3.1.2 applies. How liable that setup is to introduce a "potential, generally earth potential" is a little debatable. The insulated section is outside.
I've always taken the "insulated section at the point of entry" to mean that it had to enter in plastic so no potential introduced inside can be conducted outside.
 
Last edited:
It is my understanding that to be an extraneous conductive part, it has to have the ability to "bring in" a connection from the local earth/ground , a conductive part merely going out of a property doesn't do that.

So a metal window frame is both inside and outside, but doesn't contact the local earth/ground so no bonding. Similarly a lpg connection to external cylinders doesn't - but if said connection went underground to say a large tank/cylinder then it would.

In this case (op) I believe it does need bonding - at the point of entry, which in this case isn't at the meter.

The op indicates that the copper pipe goes into the property, and through solid flooring - i.e. does connect to earth/ground in which case the point of entry from the earth/ground is within the property where it exits the ground and needs bonding at that point.

Edit, forgot to add

You can measure the resistance between the conductive part and ground, if this is low, then it must be extraneous somehow, if 22/23kohm then it isn't extraneous.

(Need to remove the boiler earth etc as the interior pipework is likely to make a circuit via the CPC to the boiler, gas fire, cooker etc - for the test only)
 
Last edited:
Looks like painted copper to me.

There’s an air brick. Can’t you fish from there to an accessible point under the floor?

What about running the wire externally?
It is painted copper where it enters the house but feeding the meter it is plastic.

I think I will be able to get under the floor, the customer (a plumber) believes there is no way through. Obviously I need to prove him wrong.

I'm going to test it to see if it is extraneous as if the pipe is plastic then it most likely won't be. But it is in the ground (all be in in a box) and the section entering the house is metal.
 
It is my understanding that to be an extraneous conductive part, it has to have the ability to "bring in" a connection from the local earth/ground , a conductive part merely going out of a property doesn't do that.

So a metal window frame is both inside and outside, but doesn't contact the local earth/ground so no bonding. Similarly a lpg connection to external cylinders doesn't - but if said connection went underground to say a large tank/cylinder then it would.

In this case (op) I believe it does need bonding - at the point of entry, which in this case isn't at the meter.

The op indicates that the copper pipe goes into the property, and through solid flooring - i.e. does connect to earth/ground in which case the point of entry from the earth/ground is within the property where it exits the ground and needs bonding at that point.

Edit, forgot to add

You can measure the resistance between the conductive part and ground, if this is low, then it must be extraneous somehow, if 22/23kohm then it isn't extraneous.

(Need to remove the boiler earth etc as the interior pipework is likely to make a circuit via the CPC to the boiler, gas fire, cooker etc - for the test only)
I also believe it doesn't need doing and as I replied above I think I could do it.

I just took this picture on an initial visit to the job and thought it was quite interesting and would get some other opinions.



I wonder whether I could get the the customer (who as I mentioned was a plumber) to replace the bit entering the house or put a plastic sleeve around it..?
 
If there's a metal pipe leaving the house, however short, it needs bonding.
If there's a problem easily getting a bond there then I'd rather see bonding to the gas somewhere that nowhere, and there is a clause in the regs that says "as near as practicable to the point of entry".
I've seen bonding run a long way around the outside of a property too, it doesn't have to take the shortest path.
So maybe having a good hunt for the easiest place to get a bond on it is the way forwards. A common possibility is extending the bond (appropriately) from where the water is bonded on to the gas intake of the boiler.
That bit of metal leaving the house and the fact that the meter is below ground is whats causing me some debate, hence the question to see what people thought.
I'm sure I could bond it, there is always a a way.
 
That bit of metal leaving the house and the fact that the meter is below ground is whats causing me some debate, hence the question to see what people thought.
I'm sure I could bond it, there is always a a way.
But if the copper pipe goes through a solid floor, then bond is required at the point it enters the property from this solid floor, not at the meter
 
But if the copper pipe goes through a solid floor, then bond is required at the point it enters the property from this solid floor, not at the meter

I think the copper pipe just goes straight through the wall though, and not via any solid flooring?
 
I think the copper pipe just goes straight through the wall though, and not via any solid flooring?
"The customer doesn't want the disruption as there is a bathroom between and a semi solid floor"

From the original post.

Ps. Why can't I quote from the original post - I can from all the replies?
 
"The customer doesn't want the disruption as there is a bathroom between and a semi solid floor"

From the original post.

Ps. Why can't I quote from the original post - I can from all the replies?

Mmm, not clear on this. I thought he meant the solid floor was the reason he couldn't get the bond from the consumer unit to the outer wall. Could be wrong. But the airbrick suggests floating floor where the pipe enters.
 
If the first place that the gas pipe is meaningfully accessible is after the solid floor (and before connection to something or a branch to more somethings such as boiler, cooker, etc,) that would be a reasonable place to bond.

AFAIK all internal gas pipe work is metal, not necessarily designed for good electrical bonds, but almost certainly a decent conductor so a bond there should do the job of ensuring the gas appliances remain at the same potential as the house CPC system and you don't roast the boiler's 0.75mm CPC under open-PEN cases, etc, etc.
 
Last edited:
(Need to remove the boiler earth etc as the interior pipework is likely to make a circuit via the CPC to the boiler, gas fire, cooker etc - for the test only)
I suspect that is often impractical as older systems have metallic pipes for hot/cold water so I really doubt you could truly electrically isolate a gas boiler's supply pipe without the assistance of a wet pants.
 
I suspect that is often impractical as older systems have metallic pipes for hot/cold water so I really doubt you could truly electrically isolate a gas boiler's supply pipe without the assistance of a wet pants.
Possibly, however the only connections between the hws and incoming water is often at the header tanks (often plastic so isolated) and where there is a mixer tap (or steel sink), or of course supplementary bonding.

So yes there is sometimes no realistic way of checking without disconnecting far too many paths to be worthwhile.
 
Mmm, not clear on this. I thought he meant the solid floor was the reason he couldn't get the bond from the consumer unit to the outer wall. Could be wrong. But the airbrick suggests floating floor where the pipe enters.
The term "semi solid floor" came from the customer. I got the impression he meant a concrete floor but agree the airbrick would indicate otherwise. He could of meant dwarf walls below...
I would agree it looks like its going in above the floor. There were units along the wall behind so I did not get a proper look
I will be going back to do some work (likely in January) and bonding this if it turns out it needs it.
Further investigation is definitely required on all aspects.
 

Reply to Gas bond, plastic pipe but metal into properly in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Replies
6
Views
1K
A 'Sunday challenge' for the qualified electricians.... Can anyone explain why a built-in gas meter housing box that is located 600mm above a...
Replies
8
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock