Discuss Gas Bonding Conductor in 20mm conduit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
The scenario,

Property has no bonding to gas meter. There is a 4mm T+E radial from the DB to an outside socket which is located 300mm from the gas meter (external meter). The 4mm T+E is housed in 20mm plastic conduit running along the external wall.

To prevent things looking a complete mess, any issues with running the 10mm bond inside the conduit (along with the 4mm T+E) other than it being a bit cosy ?

Thanks
 
cant see a problem with that, looks better than cable tied to the side
 
You could argue not that I would, it is not suitably supported to prevent premature collapse in the event of a fire even though it is external :)
 
4mm to a socket? Long run or the end of a radial circuit?
You would have had more room if it had just been 2.5.

Do it RAF and tie wrap it to the outside of the pipe. ;)
 
4mm to a socket? Long run or the end of a radial circuit?
You would have had more room if it had just been 2.5.

Do it RAF and tie wrap it to the outside of the pipe. ;)
No need to go to the expense of tie wraps.. just undo the saddles, shove the cable in and put saddle back. ;)

Anything you can do I can do rougher :D
 
feed inside the conduit. bit of lube ( ooh matron ). or install bonding inside house close to point of entry. sodd the gas bods with their "bond to outside meter" crap.
[automerge]1570446497[/automerge]
No need to go to the expense of tie wraps.. just undo the saddles, shove the cable in and put saddle back. ;)

Anything you can do I can do rougher :D
and paint it black to camoflage it. :
 
there's only 1 reason that gas bods want to bond in the meter cabinet. it's that theyonlyneed 1 brain cell to find it, whereas looking inside, less easily seen, requires a minimum of 4 to make a quorum.
 
4mm T&E and 10mm earth wire in 20mm conduit. I would of thought a bit tight.
Would that comply re space factor?
yes because the bonding cable is not a current carrying cable, so you can ignore it as to grouping. however, if really tight fit, it could inhibit cable cooling . in this cas a 4mm cable feeding a single socket is limited as to amperage, so i would not consider it as a problem.
 
yes because the bonding cable is not a current carrying cable, so you can ignore it as to grouping. however, if really tight fit, it could inhibit cable cooling . in this cas a 4mm cable feeding a single socket is limited as to amperage, so i would not consider it as a problem.
Wasn’t there a band in the 80’s called Tight Fit ? :cool:
 
original by Karl Denver Trio. about `1964 iirc.
 

Reply to Gas Bonding Conductor in 20mm conduit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
467
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock