Search the forum,

Discuss Gas meter earth bonding in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
When running the 10mm Main Protective bonding to the Gas in a semi recessed gas meter box, how do you enter the box with the cable?
The reason I am asking is:
1) The pipe sleeve for the gas pipe can not contain the earth as it is not 25mm separation. (yes I know it will attach to the pipe anyway).
2) The gas fitter says we can not make another hole into the box as it is not allowed.
 
you can run the bonding cable alonside the gas pipe. the 25mm separation is relevant to live conductors. (by live, i mean line and neutral.)
 
When running the 10mm Main Protective bonding to the Gas in a semi recessed gas meter box, how do you enter the box with the cable?
The reason I am asking is:
1) The pipe sleeve for the gas pipe can not contain the earth as it is not 25mm separation. (yes I know it will attach to the pipe anyway).
2) The gas fitter says we can not make another hole into the box as it is not allowed.
Fit a green earth clamp outside the box and put lots of vasoline on connections so my boyfriend said
 
Hi - this from a Voltimum article :
“BS 6891:2005 Installation of low pressure gas pipework in domestic premises, clause 8.16.2 states that gas installation pipes must be spaced at least 150mm away from electricity meters, controls, electrical switches or sockets, distribution boards or consumer units. There should also be a separation between a supply or distribution cable of at least 25mm for domestic pipework up to 35mm or 50mm for pipework over 35mm.”

Note they say supply or distribution cable, not bonding, as per @telectrix in post #3.

Q & A of the Day - How far away from a gas pipe should a cable be? - https://www.voltimum.co.uk/articles/q-day-how-far-away-gas-pipe-should
 
I don't think it's anything to do with separation, the applicable regulation is concerning suitable means of support for an electrical cable. I'm fairly certain that means independent of other services are required. I do not have the BBB to hand but will have a look and see if I can find applicable regs tomorrow.
 

Reply to Gas meter earth bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
978
We had our gas disconnected last week and the meter removed. We need to start removing the redundant gas pipes in inside the property. There is...
Replies
6
Views
2K
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock