Discuss Gas & Water bonded to 1 x 10mm cable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

544.1.2 The main protective bonding connection to any extraneous-conductive-part such as gas, water or other metallic pipework or service shall be made as near as practicable to the point of entry of that part into the premises. Where there is a meter, isolation point or union, the connection shall be made to the consumer’s hard metal pipework and before any branch pipework. Where practicable the connection shall be made within 600 mm of the meter outlet union or at the point of entry to the building if the meter is external.
 
544.1.2 The main protective bonding connection to any extraneous-conductive-part such as gas, water or other metallic pipework or service shall be made as near as practicable to the point of entry of that part into the premises. Where there is a meter, isolation point or union, the connection shall be made to the consumer’s hard metal pipework and before any branch pipework. Where practicable the connection shall be made within 600 mm of the meter outlet union or at the point of entry to the building if the meter is external.
Nice one that answered that question just right.
 
I think the continuous earth conductor bonding gas and water was in an edition of the regs from the distant past
 
The bonding conductor would still need crimping or be accessible for inspection if it were joined, you couldn't just hide a terminal block under the floor.
Also bonding should electrically be where the pipe enters the building. But gas has its own special rules about not bonding before the meter, and anyone who removes the meter is supposed to clip a temporary bond on.
 
The bonding conductor would still need crimping or be accessible for inspection if it were joined, you couldn't just hide a terminal block under the floor.

Also bonding should electrically be where the pipe enters the building. But gas has its own special rules about not bonding before the meter, and anyone who removes the meter is supposed to clip a temporary bond on.

It should, but it doesn't have to be.
 
The bonding conductor would still need crimping or be accessible for inspection if it were joined, you couldn't just hide a terminal block under the floor.
Also bonding should electrically be where the pipe enters the building. But gas has its own special rules about not bonding before the meter, and anyone who removes the meter is supposed to clip a temporary bond on.

Gas doesn't have its own special rules about bonding, bs7671 says the same thing as it does for all services, it should be after the meter.
 
Gas doesn't have its own special rules about bonding, bs7671 says the same thing as it does for all services, it should be after the meter.
fair point I meant special in comparison with generic extraneous conductive parts. but my actual point is it's not the meter that makes it extraneous it;s the fact that it enters from outside the zone, therefore the OPs gas bonding at the point of entry is actually better electrically
For example because anyone who removes the meter without temporary bonding won't be breaking any diverted neutral current in that case)
 

Reply to Gas & Water bonded to 1 x 10mm cable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
1K
Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
Replies
1
Views
315
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock