I have a single phase motor showing the following information

P2 0.18Kw 50Hz
230 Volts
1.70Amps
Cos 0.97

How does the 0.18Kw work out?

My working is P=I*V*PF - P=1.70*230*0.97
P=379.27w not 1.8Kw

Help please!
 
Your calculation gives the input electrical power, but P2 is the output mechanical power of 180W or approx. 1/4 hp, so you also need to multiply by the efficiency to get this figure.
 
A common missing factor in motor calculations is efficiency and it seems this hasn't been included in yours..

KW= I x V x PF x Eff

or

I = KW / (V x PF x Eff)

As you don't have all the info here then you equation will be out, by what margin depends on the motor and its normal losses.
 
My working is P=I*V*PF .
You forgot efficiency P=I*V*PF*Efficiency. I also think they're being very optimistic with the PF as 0.97 as well. Finally they stated the output as 0.18kW, not 1.8kW that you stated after your calculation.

**edit** Oops, only saw the first reply before I posted.
 
Last edited:
Your calculation gives the input electrical power, but P2 is the output mechanical power of 180W or approx. 1/4 hp, so you also need to multiply by the efficiency to get this figure.

So, does these mean that the motor has an efficiency of 0.47Nm?

Nm=P out/P in

Nm=0.18/0.379

Nm=0.47Nm
 
The efficiency calc is correct but your units are suspect.

Nm would usually be used to express Neuton Meters which is a measure of torque and not a unit of efficiency.

η Is the lower case Greek letter eta, not the normal English letter n. η[SUB]m[/SUB] is used to denote efficiency and isn't a unit of it....if that makes sense.

Efficiency is a ratio and it doesn't have any units.
 
Last edited:
The efficiency calc is correct but your units are suspect.

Nm would usually be used to express Neuton Meters which is a measure of torque and not a unit of efficiency.

η Is the lower case Greek letter eta, not the normal English letter n. η[SUB]m[/SUB] is used to denote efficiency and isn't a unit of it....if that makes sense.

Efficiency is a ratio and it doesn't have any units.

Thanks for that explanation.

So if I understand this correctly, would I be correct in saying :-

This motor is rated as having an output of 0.18kW, however due to it's efficiency (or inefficiency) uses 0.379kW of power to work.
 
Thanks for that explanation.

So if I understand this correctly, would I be correct in saying :-

This motor is rated as having an output of 0.18kW, however due to it's efficiency (or inefficiency) uses 0.379kW of power to work.

I think your confusion here is you trying to match 2 different meanings... A 0.18KW motor refers to the mechanical energy output available at the shaft which is sometimes given in horse power (which is less confusing), the KW rating of a motor is not the electrical wattage that is used to power the motor so a 1kw motor will not use 1kw of electrical energy at full load.
 
Last edited:

Reply to General help on a single phase motor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
808
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
562
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
689
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock