Iona222

Trainee
Reaction score
41
Seen a consumer unit hager today, was old, the mcb had a little door on it, I opened one and it had a 3a plug fuse in it. Are they for storing stuff. Whats the low down with them? Cheers.
 
You mean these? Still available, but rare in domestic usage now. Flat I was in today still has them for the off peak circuits (Memora 2000 brand). Easier to replace than fuse wire, certainly - though not always that easy to find off the shelf...

I believe there are occasions in commercial/industrial scenarios where fuses have an advantage over MCBs still (not sure when though).
 
You mean these? Still available, but rare in domestic usage now. Flat I was in today still has them for the off peak circuits (Memora 2000 brand). Easier to replace than fuse wire, certainly - though not always that easy to find off the shelf...

I believe there are occasions in commercial/industrial scenarios where fuses have an advantage over MCBs still (not sure when though).
Ye them, is it for storing fuses. Seems odd.
 
Ye them, is it for storing fuses. Seems odd.
Nope, they are just fuse carriers - the fuse is the protective device, just as fuse wire was. Still valid in BS1761 in suitable circumstances - BS3036

Unless you mean the spare cartridge box - which looks like it could be fitted into a unit to store spare fuses for the remaining ways?
 
the old mem fuse boards with the dumpy fuses still loads of them in my area , some even have a front up rcd as the main switch

I once pressed the test button on one and it went bang blowing up the internaLs and the switch went floppy like a month old lettuce leaf
 
You mean these? Still available, but rare in domestic usage now. Flat I was in today still has them for the off peak circuits (Memora 2000 brand). Easier to replace than fuse wire, certainly - though not always that easy to find off the shelf...
The rewirable fuses came first in electrical history, and newer BS3036 versions have continued in use still today, but they have several big down-sides:
  • Replacing wire needs some skill, and often the public lacks that (especially as often it was the 5A lights circuit that went, at night, so dark and trying to fiddle with the little wire-retaining screws)
  • Following from the above, folk would often put in the wrong wire, either by mistake or deliberately to "stop it blowing so often", with potentially serious effects.
  • Inserting or withdrawing a fuse on load can end very badly, so again a bit of skill or sense to follow that warning is needed.
  • Those fuses have very limited breaking capacity as nothing specific to quench the arc that forms when the wire blows.
Quite early on the HRC fuse was developed with the wire in a ceramic tube and filled with arc-quenching sand. Just think how far back BS88 originated from the number alone!

These HRC fuses solved the breaking limit for most situations, upping from a couple of kA to hundreds of kA as needed, and as a plug-in (or bolt in) device were a little simpler to change. The problem of interchanging fuses in the domestic (low or non-skilled user) case was sort-of tackled by the likes of BS1361 where different fuse ratings have different body sizes, unlike BS88 where you get a big range in an identical body.

But still the fuses have two real issues, especially for domestic use:
  • Changing under load (or using to isolate) can be dangerous
  • If one blows often nobody has a spare, and its at night and shops closed.
So they had a short period of popularity from the workhorse of BS3036 until the arrival of reasonably priced MCB, at which point you really would not use a fuse for any domestic CU (though we still have them in 13A plug and FCU, of course).

I believe there are occasions in commercial/industrial scenarios where fuses have an advantage over MCBs still (not sure when though).
The HRC fuses like BS88 has some advantages over MCB and MCCB that make them still a popular choice in an overall system design:
  • In general, fuses have much better energy-limiting capabilities at high PFC than MCB or MCCB. Good for cable adiabatic, as well are reducing the risk of arc-flash / arc-blast injuries to anyone working live.
  • Due to the smooth time/current curves, fuse-fuse cascades can achieve total selectivity at ratios of 1.6:1 to 2:1 in a distribution system.
  • When feeding a MCB, a suitable fuse can still achieve sufficient selectivity in practice (often at several kA fault, where as end of circuit PFC might only be a kA or so) as well as protecting the MCB from massive PFC, so long as the fuse is starting to break and thus energy-limit at the upper range of MCB safe operation (typically 6-10kA)
  • Fuses are much cheaper than MCCB. So if you don't need some of the fancy adjustable features of electronic MCCB, or its use as a means of isolation on-load, you can have a better and cheaper solution for high current distribution/protection using fuse s (for example, the Ryefield boards, or a bus-bar chamber with a few fused-switches if you need isolation/switching on load as well)
Here is an educational/advert video comparing fuses and MCCB, while it is biased towards fuses in some ways, it serves to illustrate some of the above points quite graphically:
 
Last edited:
that's 5 minutes of my (now) limited time on earth that can't be recovered. beam wake me up Scotty.
 
that's 5 minutes of my (now) limited time on earth that can't be recovered. beam wake me up Scotty.
Good job you didn't watch the video as well!

To be fair, it is both more entertaining and has a better plot than some Hollywood films I have wasted an hour and a half of my life watching...
 
Here is an educational/advert video comparing fuses and MCCB, while it is biased towards fuses in some ways, it serves to illustrate some of the above points quite graphically:
I still believe parts of that video are fake, as I did 3 years ago! The explosions cool though.
 
This for one:
fuse.png
 
That does look a bit odd.

However, given the big-names involved in both doing the demo and in the rival's equipment being tested against the fuses I suspect the results must be pretty much sound.

They don't say what the MCCB or fuse is on that test, but assuming it is something like 40A then looking at a Hager 160 series MCCB the I2t is 600k while a 40A BS88 fuse is 5k.

Up at 100A the 160-series MCCB is around 1000k (250 series around 3000k) while the BS88 fuse is 70k, so it really is a big difference in let-though energy!
 

Reply to Hager mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K
We are looking for a distribution board to provide 3 * 160A three-phase feeds, but they are basically redundant supply path options so max total...
Replies
4
Views
333
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock