say what?! Slowwwwly.....
At the incomer the cores have been split to L, N, and earth - you can see the three cables coming in.

This split concentric cable joins the N and E together - which is prohibited (joined quite well or fairly poorly depending on which outer wires are used at each end).

In effect this additional combining of pen gives the silly earthing arrangements
 
Last edited:
The split concentric cable joins the N and E together - which is prohibited (joined quite well or fairly poorly depending on which outer wires are used at each end).

No it doesn't, it keeps the N and E seperate, that's why it is called split concentric, the outer concentric conductor is split into two different conductors.
[automerge]1598035435[/automerge]
Only in certain installations, but not the way this has been done

By which rules and what installations?
 
No it doesn't, it keeps the N and E seperate, that's why it is called split concentric, the outer concentric conductor is split into two different conductors.
[automerge]1598035435[/automerge]


By which rules and what installations?
Yes, but usually they are separately identified - these don't look to do so - it could be that only one set of outer wires goes to neutral, and the other to earth, but as I see that particular instance such segregation isn't guaranteed, it looks like a random selection of outer wires split between n&e rather than proper split.

The neutral wires usually have continuous insulation, it looks to me that its sleeved - on my phone anyway
 
Yes, but usually they are separately identified - these don't look to do so - it could be that only one set of outer wires goes to neutral, and the other to earth, but as I see that particular instance such segregation isn't guaranteed, it looks like a random selection of outer wires split between n&e rather than proper split.

The neutral wires usually have continuous insulation, it looks to me that its sleeved - on my phone anyway

They are seperately identified, the blue cores insulated cores are connected to the neutral bar and the bare earth cores have been sleeved and connected to the earth bar.
 
They are seperately identified, the blue cores insulated cores are connected to the neutral bar and the bare earth cores have been sleeved and connected to the earth bar.
Perhaps it is me and my phone, but it looks like sleeving on both n&e to me, if not and it's been done correctly then I stand corrected.
 

Reply to Has anyone come across this type of cable for a submain. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
764
I get how they work and can kind of understand the reasoning, I remember the early "no-trip" RCD testers, D-LOG made one that saturated the RCD...
Replies
11
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
937
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
715
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock