Discuss Have come across a 16A Ring Final in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
29
I've not come across this before. The current regs state it should be on a 32A MCB. I've been asked to re-wire a bedroom which will involve extending this ring. It already serves two other bedrooms and the lounge. I know I probably should tell the client to upgrade this MCB to 32A, but is it necessary ? The ring is on 2.5mm T&E. It's a bit of an unusual find. The house was built in the 1930's but was rewired only recently, so I'm surprised to find such a situation.

Any thoughts ?
 
Seen loads of rings on a !6a or 20a mcb , especially on newer builds and new flats

I think some sparks do this for 2 reasons , 1 because of de-rating for insulation and 1 because they ran out of 32a devices
 
Are you sure it’s a ring?
As above… maybe it was a ring but due to a fault it’s been turned into a two branch radial.

Don’t replace it with a 32 unless you know for sure…. And quite frankly, why would you need to? 16 will be sufficient for bedrooms.
 
Are you sure it’s a ring?
As above… maybe it was a ring but due to a fault it’s been turned into a two branch radial.

Don’t replace it with a 32 unless you know for sure…. And quite frankly, why would you need to? 16 will be sufficient for bedrooms.
Getting a bit tight if there are a couple of people who like to use hair driers etc at the same time, that is up to 16A on its own.
 
I've not come across this before. The current regs state it should be on a 32A MCB. I've been asked to re-wire a bedroom which will involve extending this ring. It already serves two other bedrooms and the lounge. I know I probably should tell the client to upgrade this MCB to 32A, but is it necessary ? The ring is on 2.5mm T&E. It's a bit of an unusual find. The house was built in the 1930's but was rewired only recently, so I'm surprised to find such a situation.

Any thoughts ?
Is it a RFC? Have you tested for r1r2 and rn? R1+R2 ETC
 
Sounds like you've got daughters as well. driers, straighteners, chargers, music on full blast.....
I once went to a party as a guest and had to move several circuits onto a different phase because on top of the expected heating and cooking loads that were above and beyond normal,

8 to 10 of the fairer sex were upstairs in various rooms beatifying themselves with all of the above.
eventually they took out the 100A incoming fuse, the cable was hot to touch!
 
Getting a bit tight if there are a couple of people who like to use hair driers etc at the same time, that is up to 16A on its own.
16A for 2 hair dryers?? sure they not paint strippers.
 
bloody hell.no wonder females have frizzy hair and fried brains.
 
I've not come across this before. The current regs state it should be on a 32A MCB. I've been asked to re-wire a bedroom which will involve extending this ring. It already serves two other bedrooms and the lounge. I know I probably should tell the client to upgrade this MCB to 32A, but is it necessary ? The ring is on 2.5mm T&E. It's a bit of an unusual find. The house was built in the 1930's but was rewired only recently, so I'm surprised to find such a situation.

Any thoughts ?
Maybe a long unfused spur was added with multiple sockets so they derated it

It's not great really RFCs being dropped down to 16/20 for various reasons. Somebody comes along after and changes it up to 32
 
Maybe a long unfused spur was added with multiple sockets so they derated it

It's not great really RFCs being dropped down to 16/20 for various reasons. Somebody comes along after and changes it up to 32

If it was done by an electrician, to bypass a fault, then it’s a perfectly applicable solution.
It should have a test cert detailing the alteration, and as such, anyone else doing work to that circuit would have the information, and would not uprate the breaker.
 
If it was done by an electrician, to bypass a fault, then it’s a perfectly applicable solution.
It should have a test cert detailing the alteration, and as such, anyone else doing work to that circuit would have the information, and would not uprate the breaker.
Ah ok so the info is available

When you say bypassing a fault are u talking about removing a leg and dismantling the ring
 
As far as the OP question, we dont know if there's info regarding why its been downrated.
Either there is a break in the ring somewhere, and its been converted to 2x radials, or part of the ring has been wired in 1.5 or something, which means a 32A cannot be used.

Sorry..."bypassing" wasn't the right choice of word.
 
Quite common to find ring final circuits on 20A protective devices here. I must admit, it drives me nuts. Why go to the effort of installing and verifying a ring final circuit only to remove its primary benefit?
 
I admit that I am one of those people who fit them.
Among reasons is when wiring bedrooms with a view to alterations latter for example when there was a possibility of house being latter converted to HMO or case when we were not sure if Gas arrives and as such giving excess number of rings for potential heaters. I am of a believe that if you can make something more safe then do so and where usage is expected to be low enough for B20. I would use B20 MCB providing protection and reacting under fault condition even when current enough to blow B32. Next point is that if you lose one of the cable contacts on a ring (break the ring) and your current flows via only one cable, It limits flow.
So I disagree with a term" "upgrade" to 32.
I fit smoke alarms on B3 MCB's.
I have also previously UPGRADED ring circuit MCB from B32 to more sensitive B16 on an ocasion when older wirings Zs was too high, but insulation test was still above 120M.
NOTE: As I have previously been refered to as possible troll for being one of those people against Rings I did made an attempt to avoid criticising them in this message to avoid flame (spark)
 
Last edited:
Quite common to find ring final circuits on 20A protective devices here. I must admit, it drives me nuts. Why go to the effort of installing and verifying a ring final circuit only to remove its primary benefit?
I would chanlenge you on that As many consider primary benefit of RFC to be secondary earthing (or connection route) should the cable gets disconnection or damage along the route.
While I am not a fan of RFC myself another of the benefits greater then its maximum fuse size is that in the event of lose or limited connection the other leg will have lower resistance and as such the resulted arcing is likely to be far lower to none, where on radial where there is no parallel path all current would have have to flow through it.
 

Reply to Have come across a 16A Ring Final in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Have come accross a job where house ring run in T/E but has an old extension with earthed metal conduit used for sockets and only live and neutral...
Replies
6
Views
1K
Hi there all, I have a property and I have noticed the following wiring (please see below) in one of the rooms in the house. It looks like the...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock