Discuss Hawkesworth Testing - Anyone here work for them..? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News to me that you need a probe for class 2 ? I was lead to believe the probe was for class 1 so you could obtain an earth.

I did have a rant in another thread somewhere about the probe and class 2, you are not alone, almost every engineer I met at HW didn't know about requiring the probe which is required for the insulation test, just plugging in a class 2 and pressing the button tests nothing at all. Probably means around half a million tests per year are done incorrectly.
 
Think you need to check a Kewtech manual.No were does it state you have to use a probe for class 2 appliances.As I said it is used to obtain an earth on a class 1,that's why there is a class 1/2 test.What about the soft test?would you use a probe for that too?
 
Do you understand how a class 2 test operates? The phase and neutral are joined and act as 1 leg of the 500v, the earth probe is the 2nd leg. With no probe you are simply sending a phase to the L/N join which has no effect. The only test between L/N is a quick resistance check to see if the device is turned on or off.

Please see your Kewtech manual page 7: ᾋ PE / Class II insulation probeConnect the Test Lead with crocodile clip (M-7208) (fig 5) to this
terminal for the measurement of protective conductor resistance and
Class II insulation, and clip metal parts of the appliance under test
with the crocodile clip.

Please see page 22: It clearly shows the probe being used on a class 2 device.

If you speak to Kewtech they will advise exactly the same. In the case of a class 2 with no exposed metal kewtech advise probing a suspect weak joint on the casing or screws etc.
 
Last edited by a moderator:
Do you by any chance work for Hawkesworth main office, I notice they pretend to be a normal punters and customers in defence of anything negative? (Usually indicated by a new user with his first post about them) Im pretty sure this thread will be removed/locked before long.
 
Work for Hawkesworth!!! No mate , used too but not now. Still think what you are saying regarding class 2 is bolox. I have worked with many pat testers over the years some good and some bad.If you knew Hawkesworth engineers you may have come across C.C. who is by far their best engineer(by the book) , I have worked with him many times and never have I seen him or anyone else use a probe on class 2.So if you were to test a class2 table lamp were would you put your probe?If you were to test a class2 glue gun were would you put your probe?.....and don't tempt me!
 
It would be best to confirm with the manufacturer of the equipment the process to be followed with a class 2. As mentioned I have spoken to Kewtech (old testers) and Seaward for their new testers and both advised me of the information I have mentioned. If kewtech and Seaward tech are both wrong, and have put incorrect information in the user manuals of their own products then I stand corrected.
 
I did have a rant in another thread somewhere about the probe and class 2, you are not alone, almost every engineer I met at HW didn't know about requiring the probe which is required for the insulation test, just plugging in a class 2 and pressing the button tests nothing at all. Probably means around half a million tests per year are done incorrectly.

I know what you mean. In theory it is a completely pointless test probing a double insulated item, because you'll get infinite ohms (assumig it's not knackered), exactly what you'd get without using the probe!!! (must stop staing the obvious).

I've done PATing for 40p an item (agency work) so I know the ways of boosting your daily figures, aint worth getting out of bed otherwise!

It's all ******** anyway, last PAT job I had in a hotel, failed an iron with a broken case, put red fail sticker on it, took the fuse out, told the room manager who just happened to be passing by, 'relace that iron in room 123', ok will do. About 3 weeks later I get phone call about some guest complaining that his ****ing iron doesn't work...............I get more sense talking to the wife.
 

Reply to Hawkesworth Testing - Anyone here work for them..? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi Everyone, My first post here, just a simple question. I currently get all of my work through word of mouth and contracts that I have...
Replies
14
Views
782
Hi So after working for a company i have decided to go self employed and start my own business. people on checkatrade my builder and rated...
Replies
8
Views
491
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
960
I'm wondering if anyone has used this tool. First of all I'm an automotive electrician but my work sent me on a PAT testing course and we have a...
Replies
18
Views
2K
So I have tried applying to every electrician mate/improver jobs there is on every job websites and I got a few calls saying that they want guys...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock