Came across a heating system which had only 1x 2 port valve which was used only for the heating. There was another valve which had been disconnected from the mains but set in open position. I assume this was for the hot water.

Then From the junction box there's one three core going up to 2 x cylinders in the loft. Am i correct in thinking this is dangerous?

Shouldnt there be a valve to control hot water to cylinders
 
Suprisingly they've used the cpc for earth. Am I right in assuming they've taken perm feed from a fused spur to give permanent feed to valves along with neutral and earth. Then dropped switch live to jb next to boiler
 
Surprisingly they've used cpc as earth. Am I right in assuming they've used a permanent feed in the loft next to the cylinders then dropped three core down to jb next to the boiler?

hot water don't need a valve it can be an open loop circuit with a swlive to the boiler if the cylinder stat is in place that's fine,also as previously mentioned the temp on the boiler can be controlled there too.
 
Suprisingly they've used the cpc for earth. Am I right in assuming they've taken perm feed from a fused spur to give permanent feed to valves along with neutral and earth. Then dropped switch live to jb next to boiler
I would assume then that of the 3 cores 1 would be live from roomstat to valve 1 would be from cylinder stat(i think these go to brown on respective valves) then the 3rd core will go from orange linked from both valves which is switched live to boiler
 
post 32 so they needed 2 cores and used a 3core and earth and used the extra core as earth, sounds like you have a swl for the boiler (orange) and a swl from the programmer which is connected to a cylinder statt or its connected to a room statt.
 

Reply to Heating system with only one two port valve. Is this dangerous ... in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top