Discuss Help/Advice with Long cable runs in garden in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Domestic property



Supply number 1
6 flood lights 4x400watt= 1600 watts
250meters from board to closets corner of tennis courts

Tennis court size
23m x 10m

My calculations are suggesting a
16mmsq cable
2.4% volt drop

Would anyone have any advice for doing long distances in a garden?
  • 10-16mm to a halfway point and distribute out for both circuits
  • apply diversity?


Supply number 2
Driveway 150meters
Cable length 200meters from fuseboard to 15 bollards lights (15x5w)=75watts

calculations
230v
75 load
1.5mmsq cable
Volt drop 0.8%

Many thanks
 
Domestic property



Supply number 1
6 flood lights 4x400watt= 1600 watts
250meters from board to closets corner of tennis courts

Tennis court size
23m x 10m

My calculations are suggesting a
16mmsq cable
2.4% volt drop

Would anyone have any advice for doing long distances in a garden?
  • 10-16mm to a halfway point and distribute out for both circuits
  • apply diversity?

Presumably all of the lights will be on at once if they are for a tennis court so there is no possible diversity to be applied.

I would take a 16mm submain, if that is the required size, to a suitable enclosure at the side of the tennis court. In the enclosure I'd fit a small DB to put each of the 6 floodlight positions on its own circuit.

Having each lighting position on a seperate circuit makes future maintainence and fault finding much easier.

How will this lighting be controlled?

Having a DB at the tennis court would also allow the installation of a socket relatively easily which will probably be quite useful at some point in time.
 
Thanks for reply, Yes to all floods on a same time- so your right no diversity.
I think I’m going to try 2x lutron RA2 selects or even a Quentic wifi module.
However this plan was for having the 2 cables back at the main house where the wifi would have been strong enough. But now looks like it may have to be a wise box near the tennis court.

Presumably all of the lights will be on at once if they are for a tennis court so there is no possible diversity to be applied.

I would take a 16mm submain, if that is the required size, to a suitable enclosure at the side of the tennis court. In the enclosure I'd fit a small DB to put each of the 6 floodlight positions on its own circuit.

Having each lighting position on a seperate circuit makes future maintainence and fault finding much easier.

How will this lighting be controlled?

Having a DB at the tennis court would also allow the installation of a socket relatively easily which will probably be quite useful at some point in time.
 
You can still control it from the house by switching the feed to the tennis court if that is what is required.

Why the need for a wireless switching solution?
 
On p424 of bs7671 there is a correction calculation for operating temperature. Based on your load being nowehere near the max for the cable, it will lower your calculated volt drop, which should permit 10mm2 at 3%.

If you were prepared to allow a 5% drop, it might just about permit 6mm2.
 
If you were prepared to allow a 5% drop, it might just about permit 6mm2.
As far as I know, the 3% drop for lights was to avoid unpleasant variations in brightness as other lights are switched on the circuit, probably not so big an issue now with LED as they have less change in brightness versus voltage than filament.

However, if all lights are switch simultaneously then no such interactions and 5% might make for a far cheaper job.

But also check the surge from simultaneously switching them. Some companies give to limits for this in terms of MCB rating, also check the de-rating needed for any relay or contactor.

You can reduce the surge slightly by using a zero-crossing SSR, but do remember that such devices cannot be used for isolation, only for functional switching.
 
Customer had ask if they can control it through there phone or app

You'd think a physical switch would be more suitable wouldn't you? But I guess if you can afford a tennis court and have enough land for it to be 250m away from your house it's probably against the rules to have something as basic as a normal switch.
 

Reply to Help/Advice with Long cable runs in garden in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...
Replies
5
Views
2K
M
Hi all, very sorry to bother you with triv. I am in the process of sorting out some pretty shocking electics in a house that has been bodged at...
Replies
0
Views
3K
mbga9pgf
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock