0
I am a retired Engineer who was an electrician. My name is Stephen .
I was changing a fluorescent light in my garage and was using a mains tester as a screwdrivet when I notice it lit up when I touched the lid screw.
Once in 50 years working on breakdowns in the NHS I had came across this so put tester on main earth terminal at incomer and it lit again. I tried my pipework, cylinder and socket earth pins, all lit.
I went to CU and identified what circ. was making this happen and found a wiring fault on a citcuit of sockets which I repaired.
The house was no longer "live" but I had no earth. I believe my house is TT as it is fed with overheads from a pole in my garden. ( Recently the overheads were renewed and the neutral at the top of the pole now has an earth down the pole to a rod.)
My CU has a few circuits with mo RCD and 5 circuits on a 100ma trip.
I have banged in a rod and took an Earth Loop Impedance of 14ohms. Is this acceptable?
Could I run a cable yo the earth at the pole?
Can I try to get PME done at my incomer which is only L and N.
I'm sorry I'm a bit rusty.
Oh and I checked my incoming water supply which has pladtic pipe. My earth bond is above the plastic on the consumers side of the supply.
Help
 
IT is unlikely that the "live" was a true live as you were testing with an inappropriate tester and also you would have been shocked on starting to work on the light.
If your house was a TT system then all circuits would've been RCD protected, having some circuits not protected should mean it is not TT or that the installation was dangerously unsafe.
You are not permitted to connect to the DNO earthing, the DNO may install PME earthing (especially is the supply has been upgraded) ring and ask your supplier.
 
if you've managed to measure the EFLI, i assume you have a meter of some sort. what's the voltage L-N and also L-E?
 
IT is unlikely that the "live" was a true live as you were testing with an inappropriate tester and also you would have been shocked on starting to work on the light.
If your house was a TT system then all circuits would've been RCD protected, having some circuits not protected should mean it is not TT or that the installation was dangerously unsafe.
You are not permitted to connect to the DNO earthing, the DNO may install PME earthing (especially is the supply has been upgraded) ring and ask your supplier.


RCD’s being fitted depends on the version of the regulations the house was wired to. They were a recommendation in the 14th not a requirement.
 
I strongly recommend getting a local electrician in, maybe post your location and a member may be near by. By your post i dont think you should be investigating any further no put down intended just for your own safety and the safety of every other user of the installation within the property.
 

Reply to Help. My house metal work went live in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

As above the chest level from ground ,metal ANPR housing has no connection to earth ,it has monitors modems and a camera inside with a 230 volt...
Replies
2
Views
657
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
444
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
993
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock