I am a retired Engineer who was an electrician. My name is Stephen .
I was changing a fluorescent light in my garage and was using a mains tester as a screwdrivet when I notice it lit up when I touched the lid screw.
Once in 50 years working on breakdowns in the NHS I had came across this so put tester on main earth terminal at incomer and it lit again. I tried my pipework, cylinder and socket earth pins, all lit.
I went to CU and identified what circ. was making this happen and found a wiring fault on a citcuit of sockets which I repaired.
The house was no longer "live" but I had no earth. I believe my house is TT as it is fed with overheads from a pole in my garden. ( Recently the overheads were renewed and the neutral at the top of the pole now has an earth down the pole to a rod.)
My CU has a few circuits with mo RCD and 5 circuits on a 100ma trip.
I have banged in a rod and took an Earth Loop Impedance of 14ohms. Is this acceptable?
Could I run a cable yo the earth at the pole?
Can I try to get PME done at my incomer which is only L and N.
I'm sorry I'm a bit rusty.
Oh and I checked my incoming water supply which has pladtic pipe. My earth bond is above the plastic on the consumers side of the supply.
Help
I was changing a fluorescent light in my garage and was using a mains tester as a screwdrivet when I notice it lit up when I touched the lid screw.
Once in 50 years working on breakdowns in the NHS I had came across this so put tester on main earth terminal at incomer and it lit again. I tried my pipework, cylinder and socket earth pins, all lit.
I went to CU and identified what circ. was making this happen and found a wiring fault on a citcuit of sockets which I repaired.
The house was no longer "live" but I had no earth. I believe my house is TT as it is fed with overheads from a pole in my garden. ( Recently the overheads were renewed and the neutral at the top of the pole now has an earth down the pole to a rod.)
My CU has a few circuits with mo RCD and 5 circuits on a 100ma trip.
I have banged in a rod and took an Earth Loop Impedance of 14ohms. Is this acceptable?
Could I run a cable yo the earth at the pole?
Can I try to get PME done at my incomer which is only L and N.
I'm sorry I'm a bit rusty.
Oh and I checked my incoming water supply which has pladtic pipe. My earth bond is above the plastic on the consumers side of the supply.