Discuss Help wiring 2 lights with double switch. in the Lighting Forum area at ElectriciansForums.net

Rmlong6

DIY
Reaction score
0
Hey all,

Could I get help with wiring this double switch which will be individually switching front and back external lights.
With this switch I have a live source from consumer unit going in, and 2 separate cables going in for front and back lights.

so when I connect live in from consumer unit I would connect to live 1 in on left and then place a live loop from live in 1 left to live in 1 right To power both switches ?

with the neutral cable coming in from consumer unit would I put this in left 3 and then loop across to right 3?

with separate out going cables connect live to live 2 out with one cable and connect other cable for other light and switch to live out 2 on right ?
then neutral from cable out on left to out 3 and neutral cable from right out to out 3 on right ?

if that makes sense ?

So basically I would like a switch to front light and a separate switch to back light

cheers Rich
1B193793-1332-4AE9-893C-0B0862CD9F3B.jpeg8635561A-7252-4085-A2D0-487A5B376CF3.jpeg
 
when I connect live in from consumer unit I would connect to live 1 in on left and then place a live loop from live in 1 left to live in 1 right To power both switches ?
Yes
with the neutral cable coming in from consumer unit would I put this in left 3 and then loop across to right 3?
NO!!!! The neutral does not connect to the switch at all. Put the incoming neutral, and the neutrals to the two lights in a separate bit of insulated terminal block.
with separate out going cables connect live to live 2 out with one cable and connect other cable for other light and switch to live out 2 on right ?
Yes
then neutral from cable out on left to out 3 and neutral cable from right out to out 3 on right ?
As above. NO!!! If you connect the neutral to 3 then the fuse will go BANG.

PS what are your plans for the indicator light on the switch?
 
you’re right to a point.

The neutrals just need connected together, NOT TO THE SWITCH AT ALL!

If you connect the neutrals to 3, there will be a dead short between live and neutral when the switch is operated.

Think of this as two switches… live feed to both number 1’s. Loop between.

Switched live from one of each of the 2’s


Please remember to isolate the circuit before working on it.


With the little red light… (2 small black wires) you can leave disconnected completely or have one black wire in the neutral link, and the other black wire in with the permanent live feed, so you can see where the switch is in the dark.


Edit; beaten to it
 
Yes

NO!!!! The neutral does not connect to the switch at all. Put the incoming neutral, and the neutrals to the two lights in a separate bit of insulated terminal block.

Yes

As above. NO!!! If you connect the neutral to 3 then the fuse will go BANG.

PS what are your plans for the indicator light on the switch?
Thanks for that, I would like to keep indicator light would I leave cable in same points as it’s been placed?
with live loop going in to it?
 
you’re right to a point.

The neutrals just need connected together, NOT TO THE SWITCH AT ALL!

If you connect the neutrals to 3, there will be a dead short between live and neutral when the switch is operated.

Think of this as two switches… live feed to both number 1’s. Loop between.

Switched live from one of each of the 2’s


Please remember to isolate the circuit before working on it.


With the little red light… (2 small black wires) you can leave disconnected completely or have one black wire in the neutral link, and the other black wire in with the permanent live feed, so you can see where the switch is in the dark.


Edit; beaten to it
Thanks for that not to bothered about indicator light to much
 
I imagine lights like this:

The light fittings (the bits with the bulbs etc) need a live, neutral and earth going to them. The switches only need live and switched live.

If you basically picture the fitting as having all three wires going to it but the live has a switch in the middle of it.

So for this all you need is live into 1, link over to the other 1, and out of either of 2 or 3 to power your light. Connect neutral and earth to the neutrals and earths from the cables that run to the lights, using a wago connector or similar.

These are two way switches and if you just want basic switching you actually only need a one way version.
 
Last edited:
I imagine lights like this:

The light fittings (the bits with the bulbs etc) need a live, neutral and earth going to them. The switches only need live and switched live.

If you basically picture the fitting as having all three wires going to it but the live has a switch in the middle of it.

So for this all you need is live into 1, link over to the other 1, and out of either of 2 or 3 to power your light.

These are two way switches and if you just want basic switching you actually only need a one way version.
Thanks for that, all sorted now ?
 

Reply to Help wiring 2 lights with double switch. in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
634
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
411
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
363
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
458
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock